@ P&S,

I too am not disagreeing with the merits of RCD's, I believe they are potential life savers, in fact if you read my earlier posts on this and other threads, I have never said they should not be fitted where neccessary.
However they are not the be all and end all, nor are they the 'cure all' for all 'electrical ills', although they have their uses.

Since the 17th ed though, they have been pushed on to the domestic sector, a lot of sparks now use them as a 'magic bullet', for instance when the Zs is too high, and instead of either recalculating cable sizes or rectifying either a fault or design issues, just bung an RCD on it and it will fix it mentality, I feel over-reliance and misplaced trust has been placed on these devices. As others have said from the 16th ed and before we did not rely nearly so much on these devices.

Good luck with your experiment.
 
You are right, a large degree of faith is put on the inspector, I would always code a circuit supplying downstairs sockets with no rcd as a c2 now, recommend fitment of rcd or rcd socket nearest door. However the electrical installations were pretty safe without them, therefore I usually make recoomendations and observations but I will not insist on fuseboard replacement etc.

IMO bathrooms are pretty safe with good supplementary bonding in place and RCD's are regarded by some as a 'magic bullett' more so, reading on here, by the domestic sector.

You have to remember, houses (especially flats) were commonly wired with no RCD's right up to 2008, and were considered safe, they have not turned in deathtraps overnight!

I understand your stance in how you code installations without rcd's and its your choice as the inspector but.......
you need to consider the implications from automatically giving code 2's to rcd free installations.
many , many properties that are otherwise safe will recieve unsatifactory EICR's and will place a large financial burden on those on the recieving end.
just a thought.
 
@ P&S,

I too am not disagreeing with the merits of RCD's, I believe they are potential life savers, in fact if you read my earlier posts on this and other threads, I have never said they should not be fitted where neccessary.
However they are not the be all and end all, nor are they the 'cure all' for all 'electrical ills', although they have their uses.

Since the 17th ed though, they have been pushed on to the domestic sector, a lot of sparks now use them as a 'magic bullet', for instance when the Zs is too high, and instead of either recalculating cable sizes or rectifying either a fault or design issues, just bung an RCD on it and it will fix it mentality, I feel over-reliance and misplaced trust has been placed on these devices. As others have said from the 16th ed and before we did not rely nearly so much on these devices.

Good luck with your experiment.

Wonder how many sparks would L-N loop impedance when wedging a 30ma rcd on an overly long/poor condition circuit, chances are with 1.0/1.0 T+E It may not even trip within the disconnection times on a short circuit!

BIFF- I'm advocating not automatically giving C2's to RCD free installs! I only apply what is in the regs, and even then I only usually reccommend an rcd socket to be fitted by the back door!
 
P&S,
If you do decide to carry out your experiment, FFS please wear suitable PPE, a full visor and gloves as a minimum, we don't want you to lose an eye, or get scadded off of exploding molten plastic.
 
Wonder how many sparks would L-N loop impedance when wedging a 30ma rcd on an overly long/poor condition circuit, chances are with 1.0/1.0 T+E It may not even trip within the disconnection times on a short circuit!

BIFF- I'm advocating not automatically giving C2's to RCD free installs! I only apply what is in the regs, and even then I only usually reccommend an rcd socket to be fitted by the back door!

You implied that you were with the comment
"I would always code a circuit supplying downstairs sockets with no rcd as C2 now"
????
Sorry but that goes against current guidance.
An actual exterior socket without rcd is a code 2 but any other indoor socket without rcd is a code 3.
 
P&S,
If you do decide to carry out your experiment, FFS please wear suitable PPE, a full visor and gloves as a minimum, we don't want you to lose an eye, or get scadded off of exploding molten plastic.
Good idea ! Wont need to actually hold the blow lamp, but will be holding the camera.
If i dont get called out, will try it Saturday morning.
 
You implied that you were with the comment
"I would always code a circuit supplying downstairs sockets with no rcd as C2 now"
????
Sorry but that goes against current guidance.
An actual exterior socket without rcd is a code 2 but any other indoor socket without rcd is a code 3.

Well, the guidance book I got says C2 for sockets likely to supply mobile equipment outdoors, c3 for others. If it was a flat without garden or upstairs flat I would c3 for all sockets, if it was a flat with garden would give C2 and reccomend fitting rcd/rcd socket. My company gives the guidance on the coding and this what they put, It was a Code 2 before the EICR but still pass. Now its a fail.
 
Why complicate the issue with all the talk of upstairs / downstairs flats , garden / no garden ?
Any socket near an opening window can be potentially used for outside with an extension lead.
And if theres a choice of 2 / 3 / 4 sockets near to an exterior door youre in effect condeming the whole ring main to a code 2 defect anyway.
 
Why complicate the issue with all the talk of upstairs / downstairs flats , garden / no garden ?
Any socket near an opening window can be potentially used for outside with an extension lead.
And if theres a choice of 2 / 3 / 4 sockets near to an exterior door youre in effect condeming the whole ring main to a code 2 defect anyway.

Because an upstairs flat with no garden is unlikely to use equipment outside?
Its up to you what you code and I certainly don't disagree with your reasoning!
 
Fair enough mate , but it does worry me that your company gives you direction on how to code defects instead of letting you , the inspector , make that judgement call on a case by case basis.
If your company benefits from ensuing remedial works then a case for conflict of interests could be made against them , if you see
my point ?
 
Fair enough mate , but it does worry me that your company gives you direction on how to code defects instead of letting you , the inspector , make that judgement call on a case by case basis.
If your company benefits from ensuing remedial works then a case for conflict of interests could be made against them , if you see
my point ?

Umm.. certainly get your point, The advice they give is guidance though and I can, and regularly do, change it. They and especially I do not care about remedial works, I don't want to be doing them! I just test and record what I find, I never put down 'reccomend new board' even for wooden backed rewireables, as I believe most houses are fixable with a few minor repairs, and its not up to me to push for remedial work, only to record what I find
 

Reply to EICR and unnecessary work? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

I think it is a good idea in general, it provides a form of proof that the landlord has provide access to the required documents. further to that...
2
Replies
19
Views
1K
This fella puts his face to it about halfway through, he has an opinion on the very subject.
Replies
42
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top