Before you can decide on a Code you need to understand the consequences if not rectified the fault is posing to persons and/or property. To do this you need to understand the fundamental principles of how a circuit and circuit protection act together and how the fault will affect this partnership. Two of the biggest hazards with circuit fault are electric shock and fire, you need to decide how the fault is going to affect the circuit and the possible consequences.
 
With the Zs above the minimum value what will possibly happen if a line to earth fault occurs. Who or what is at risk and why.
 
Sometimes the best way to understand is take an extreme example. Assuming there are no rcds in play, what if your Zs was 10 ohm and you have a 40A protective device what will happen with a line to earth fault.
 
I thought the forum is to ask questions
Agree, but surely you would, I hope agree, that blatantly admitting asking questions to help pass an exam, is no help at all, after all every day is a learning day.
 

Reply to Eicr codes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
434
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
936
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
892

Similar threads

Personally, I would just put them in the observations, the inspection schedule is not exhaustive.
Replies
1
Views
204
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top