just to hijack the thread, apologies to anyone and everyone, had this today on a EICR.. 3 x 3 phase DBs along with 3 x 3 phase henley blocks mounted on a 4ft. x 4ft. ply board. board rotted away due to a leaking drain (since fixed). getting to the point where the equipment will be held up by the cables. all 3 boards have SWA cables (correctly glanded) along with a load of T/E. can't see any danger so giving it a C3 with the caveat that if it deteriorates any more it would escalate to a C2. your thoughts, gents.
 
just to hijack the thread, apologies to anyone and everyone, had this today on a EICR.. 3 x 3 phase DBs along with 3 x 3 phase henley blocks mounted on a 4ft. x 4ft. ply board. board rotted away due to a leaking drain (since fixed). getting to the point where the equipment will be held up by the cables. all 3 boards have SWA cables (correctly glanded) along with a load of T/E. can't see any danger so giving it a C3 with the caveat that if it deteriorates any more it would escalate to a C2. your thoughts, gents.
Picture??
 
just to hijack the thread, apologies to anyone and everyone, had this today on a EICR.. 3 x 3 phase DBs along with 3 x 3 phase henley blocks mounted on a 4ft. x 4ft. ply board. board rotted away due to a leaking drain (since fixed). getting to the point where the equipment will be held up by the cables. all 3 boards have SWA cables (correctly glanded) along with a load of T/E. can't see any danger so giving it a C3 with the caveat that if it deteriorates any more it would escalate to a C2. your thoughts, gents.
If everything mounted was secure then there is no code in my opinion but I would maybe put something in the covering letter to say about the degradation of the wood in which the equipment is mounted to.
 
If everything mounted was secure then there is no code in my opinion but I would maybe put something in the covering letter to say about the degradation of the wood in which the equipment is mounted to.
exactly what i done. even if the board gets worse, the cables will hold the gear up without undue stress. gave it a C3.
 
it is secure at the moment, but any further deterioration of the ply board would leave the DB supported by the cables, some of which are SWA, correctly glanded and supported .
 

Reply to Eicr codes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
434
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
936
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
892

Similar threads

Personally, I would just put them in the observations, the inspection schedule is not exhaustive.
Replies
1
Views
204
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top