marcuscrackus

I have a EICR coming up where I am sure there is no CPC in the lighting circuit, the property is rented and I am sure all the outlets are class 2. Where do i stand?

Should the circuits be rewired?

C2 or C3?

Thanks
 
If there are enclosures or accessories which require an earth then it is C2 as fault protection is not provided. The only way to resolve it is to rewire or eliminate items which need an earth. If an earth is not required and you will have to be certain then maybe C3 but that is up to you. What do you mean where do you stand.
 
What i meat was regarding the satisfactory or unsatisfactory and what remedials would need to be done. If all the outlets are class 2 so there is no way that any indirect ordirectt contact could be made and the a C3 is noted on the cert could it get away with being satisfactory? i know in an ideal world the circuits should be rewired but legally should they be?
 
That would be your call but you haven't tested it yet and lack of cpcs may be the least of problems because surely there may be other issues. Don't be blinded by one issue.
 
ok basically if there is no cpc in the loghting circuit. but all outlets are class 2 can it be left or does it have to be replaced? the property is rented.
 
You need to go and determine what is actually installed before making any coding suggestions.

Best practice guide 4 is a useful read.
 
^^

Hum... A rewire may seem sensible but this may not be necessary to get a satisfactory report.....

You can't go round coding to get work.

Just saying
 
I saw the same issue recently, but someone had tapped into a socket to run a cpc to the only light fitting that actually needed one. The run didn't look particularly easy either. If I was going to go to that sort of length I'd probably prefer just to rewire the circuit and do a proper job. On an EICR, it's a judgement issue, think it was the NIC who endorsed putting a sticker on the CU and ensuring class 2 fittings only, it is a solution, not one I'd necessarily subscribe to myself.
 
Ah yes there is the solution fit another unendorsed sticker notifying the uninitiated, assuming they can speak/read English, job done.
Wonder how long it will take the IET to publish 7671 in various languages?
 

Reply to EICR for a rented property with cpc on the lights. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My latest trick for this....if completely desperate and you have 3 very short cables .... Make a hole big enough for a quickwire to fit through...
Replies
8
Views
792
Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top