I have run 10mm2 3 core SWA to garage CU but miscalculated the length and no way Im going to reach the house CU. I need to extend the cable, is it acceptable to do it like on the picture?
Screenshot 2024-12-28 at 15.46.44.png
 
What about taking the SWA to its own little CU and split the incoming tails with Henley blocks?
House CU can be isolated without affecting garage
 
I have run 10mm2 3 core SWA to garage CU but miscalculated the length and no way Im going to reach the house CU. I need to extend the cable, is it acceptable to do it like on the picture
Yes that would be acceptable if single insulated cables are going to be exposed then put them in some containment.

A torpedo would probably be the easiest, even if you have to cut the feed cable back so that the join is in the best place.

It would also mean that the Swa can be glanded properly into the CU instead of having to use a junction box.
 
Last edited:
What about taking the SWA to its own little CU and split the incoming tails with Henley blocks?
House CU can be isolated without affecting garage
Thanks of the idea, I will have an electrician replacing my house CU at some point next year, so will definitely consider this option. At the moment I am looking for a temporary solution (as simple and cost effective as possible) and wanted to know if the one I suggested is acceptable and safe
 
Yes that would be acceptable if single insulated cables are going to be exposed then put them in some containment.

A torpedo would probably be the easiest, even if you have to cut the feed cable back so that the join is in the best place.

It would also mean that the Swa can be glanded properly into the CU instead of having to use a junction box.
I would definitely go for it but my CU in an old one with the back entry and no slots to gland SWA. I will do it properly when I replace the CU next year. Thank you
 
Yes that would be acceptable if single insulated cables are going to be exposed then put them in some containment.

A torpedo would probably be the easiest, even if you have to cut the feed cable back so that the join is in the best place.

It would also mean that the Swa can be glanded properly into the CU instead of having to use a junction box.
Is 10mm² 3 Core HO7RNF suitable to be used instead of single insulated cables in a containment?
 
Is 10mm² 3 Core HO7RNF suitable to be used instead of single insulated cables in a containment?
Yes that would be ok.

The 6181Y wouldn't have to be in containment as they are double insulated.
 

Reply to the thread, titled "Extending SWA garage cable" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
essex

Thread Information

Title
Extending SWA garage cable
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
Luka,
Last reply from
Luka,
Replies
22
Views
1,031

Advert

Back
Top