External earth fault loop tt system | Page 9 | on ElectriciansForums

Discuss External earth fault loop tt system in the UK Electrical Forum area at ElectriciansForums.net

B

brightspark2010

Evening all could anyone please tell me the the maximum ze for tt systems the jobs entail Rec cut out fuse bs88 16a to feed 1x 30 ma rcd fuse spur for feeding socket outlet what should the max ze be please
 
Max 1667 ohms is so no more than 50 volts can appear on earthed metalwork.
Anything above 200 ohms is classed as unstable and likely to increase in frozen or dry soil conditions.

As has been said, fine while the RCD is functioning!!! lol!! You'd need to go down a lot more than that for a stable system, ...believe me!! Your ground/soil conditions would be absolute crud, to go down any depth and end up with just 200 ohms!! lol!!
 

Reply to External earth fault loop tt system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
328
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top