dayrider3883
I have installed a fan from the lighting switch to bathroom do i need to use a spur for the fan or can i go direct
Discuss fan in bathroom in the Australia area at ElectriciansForums.net
both. this means fusing down before the light.But if it is a delayed fan where 2 live are used perminent and switch wire which one is fused down
Wouldn't comply with BS7671, as the whole circuit requires RCD protection, not just the part that enters the Bathroom.If the property hasn't got RCD protection, take the loop (before the light) into a FCU RCD, then out to the light, fan, etc. This way you can fuse down and have it all RCD protected. Nice and easy.
I think the regs should make an isolation switch for the fan mandatory!
but if you use the bathroom light switch to trigger the fan and the lighting is rcd protected and the fan is wired in 1.5 same as lighting then the lighting mcb should protect the fan wiring the fuseboard is next to the bathroom
Yes it's a common misconception, although I believe that it's deliberate attempt to circumvent the Regulations, as using an RCD FCU is often a lot easier than providing RCD protection for the whole circuit.Really. Live and learn, so in the case of a spur from a ring why can we get away with a RCD FCU then sockets. At least I've been adding RCD protection and isolation switching - unlike MANY I see around here!
Reply to fan in bathroom in the Australia area at ElectriciansForums.net