dayrider3883
I have installed a fan from the lighting switch to bathroom do i need to use a spur for the fan or can i go direct
Discuss fan in bathroom in the Australia area at ElectriciansForums.net
JUD the fault current won't only take the path of least resistance, it will be distributed across all paths according to their resistance.A fault current on a part of the circuit before the RCD will take the path of least resistance i.e back to earth through the cpc and along the normal earth fault loop path and, if Zs for the circuit is within limits which it should be, take out the main breaker/fuse.
I was under the impression you'd both decided to agree to disagree!
Maybe the mods should step in!
:19:
If an existing circuit of a location containing a bath or shower is extended, at least the extended part of the existing circuit must be provided with RCD protection. Supplementary bonding in a bathroom or shower room must be provided unless all the requirements in the 17th Edition for the omission of supplementary bonding are met.
The IET do, and it is that the the circuit requires RCD protection.I thought the info in the link to the ESC website I provided would have made mine and others cases.
spin, I agree with Murdoch, let's just agree to disagree.
At the end of the day only the IET could give a definitive answer as to what is required.
The ESC or NICEIC do not write the Regulations.However back to the original op, the following extract taken from ESC and Niceic Guidlines
Reply to fan in bathroom in the Australia area at ElectriciansForums.net