I have installed a fan from the lighting switch to bathroom do i need to use a spur for the fan or can i go direct
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss fan in bathroom in the Australia area at ElectriciansForums.net
You must ensure that the addition or alteration complies with BS7671.Good point, I thought you just had to make additions on older installations comply such as RCD sockets etc..and you were not obliged to upgrade the whole circuit?
You don't, you take one live to the fuse, and two lives from the fuse.but how can you take both lives into a 3 amp fuse
You don't, you take one live to the fuse, and two lives from the fuse.
Wherever RCDs are placed in a position other than at the origin of a circuit, there is danger that an earth fault between the origin of the circuit and the RCD will bypass the RCD.Back to my point, which is by using a FCU RCD and using this to supply the lights, fan and sometimes a shaver point the RCD is protecting all the circuits of the location i.e. in the said bathroom. PLUS there is a single point of isolation too.
There are too many homes around that don't have RCD's so IMHO my solution is certainly in the spirit of the regulation.
Got my Elecsa annual coming up so I might well ask him for his interpretation!
Yes it's a common misconception, although I believe that it's deliberate attempt to circumvent the Regulations, as using an RCD FCU is often a lot easier than providing RCD protection for the whole circuit.
701.411.3.3 Requires: "Aditional protection shall be provided for all circuits of the location, by the use of one or more RCDs having the characteristics specified in Regulation 415.1.1."
Which translated means all circuits supplying a location containing a bath or shower shall have 30mA RCD protection.
They've re-worded the Regulation in the amendment to only refer to LV circuits. We were hoping that this re-wording would have allowed the use of SELV equipment without the supply circuit having to be RCD protected, if the source of SELV was outside of the location. Unfortunately such is not the case. RCD protection is still required for the LV part of a SELV circuit, even though it will be as much use as a chocolate tea pot.
Appendix 15 whilst only being informative, indicates that circuits start and in the case of RFCs finish at DBs.My interpretation is that if you supply the bathroom lighting from an RCD FCU attached to the original lighting circuit then this creates a new circuit starting at the FCU as that is now the protective device for that circuit.
As it also incorporates an RCD then IMO it complies with all relevant regs.
According to BS7671, the origin of a circuit is not neccessarily at the overcurrent device.The origin of a circuit is at an overcurrent protective device. In this case that overcurrent protective device is the FCU.
Haven't you ever wondered why the regs give max Zs values for 3 and 13A BS 1362 fuses.
You are mistaking the origin of a circuit with the origin of an installation.
According to BS7671, the origin of a circuit is not neccessarily at the overcurrent device.
Regulations 433.2.2 434.2.1 indicate that devices can be installed along the run of a conductor, within 3m.
Whilst the definition of a circuit in Part 2: "Circuit. An assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective device(s)."
Indicates that a circuit is protected by the same protective device, it does not indicate that the protective device is the origin of the circuit.
However the definition aside, the fact remains that Appendix 15 informs us that the origin of a circuit is at a DB, not at an FCU.
Wouldn't comply with BS7671, as the whole circuit requires RCD protection, not just the part that enters the Bathroom.