I have installed a fan from the lighting switch to bathroom do i need to use a spur for the fan or can i go direct
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss fan in bathroom in the Australia area at ElectriciansForums.net
Carefull, you don't get splinters.i'm sitting on the fence on this one. both arguments hold water. maybe an adjudicator is required here. Widdler?
I am well aware that the definition of a circuit does not state that the protective device has to be at a DB.
I quoted the Definition to point out that a OPD is not considered to be the origin of a circuit.
Appendix 15 is not an example of typical socket-outlet circuits.
It sets out options for the design of ring and radial final circuits for houshold and similar premises in accordance with Regulation 433.1, using socket-outlets and fused connection units.
I accept that an FCU meets the requirements of an OPD as far as the definition of a circuit is concerned.
However the particular circuits we are discussing, are final circuits, and the requirements for final circuits are not just restricted to the definition of a circuit in Part 2 and those of Regulation 433.1.
Regulation 314.4 states: Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board. The wiring of each final circuit shall be electrically separate from that of every other final circuit, so as to prevent the indirect energizing of a final circuit intended to be isolated."
Now unles you are suggesting that the FCU, the light, the fan and associated wiring are not a final circuit, or that an FCU is a distribution board; how can having the origin of a circuit being an FCU meet the requirements of Regulation 314.4?
We are discussing 314.4.Regulation 314.4 isn't what we're discussing here. That is separation of final circuits.
Nowhere have I said that an FCU is a distribution board. The supply side of the FCU is connected to a final circuit that is fed from a distribution board.
What I'm saying is that the cable coming off the load side of an FCU is it's own circuit with the BS 1362 fuse as it's protective device.
Let me ask you this. On a schedule of test results what would you enter as the protective device for the lights and fan in the bathroom. You couldn't put the one at the distribution board as that is not the primary protective device for that wiring. Therefore you would have to enter it as a separate circuit and the protective device would be BS 1362.
You can do that ezzzekiel, but I would expect it to be noted as a departure on any certification, and I would further expect you to ensure that it provides the same degree of safety as would be achieved by compliance with the Regulations.Rcd fcu for your part of the works job done
The extractor fan doesn't neccessarily need an isolator.
Please read:
Bathroom extractor fans and 3 pole isolation, a source of much controversy
We are discussing 314.4.
314.4 requires that where there is more than one final circuit, each final circuit must be supplied from a separate way at a distribution board.
If 'the cable coming off the load side of an FCU is it's own circuit', then what kind of a circuit is it?
If it is a final circuit, then it does not comply with BS7671, as it is not supplied from a separate way at a distribution board.
If it is a distribution circuit, then it must be supplying either a DB or switch gear.
Is it supplying a DB or switchgear, or is it some other kind of circuit which is not defined in BS7671?
When we test continuity of RFC conductors, we are required to record the highest measured value of R1+R2. The measurements are taken at each point on the RFC including any spurs, and the highest reading recorded.
We do not record the highest value measured on the RFC, and then list spurs as separate circuits and record their values separately.
As for your question, I would treat the whole circuit as one circuit, I would not attempt to separate the lighting circuit into two circuits, one for the lights and another for the bathroom light and fan.
As such I would list the lighting circuit protective device as the protective device.
You can do that ezzzekiel, but I would expect it to be noted as a departure on any certification, and I would further expect you to ensure that it provides the same degree of safety as would be achieved by compliance with the Regulations.
It may well be the third time that you've asked the question, I'm still struggling to see it's relevance.This is the third time I've asked this and you haven't even mentioned it.
WHY, if you can't have a circuit using a BS 1362 fuse, do they provide Zs values for them in the regs. I've never seen a distribution board with 3A and 13A plug-top fuses in them.