D
dayrider3883
I have installed a fan from the lighting switch to bathroom do i need to use a spur for the fan or can i go direct
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss fan in bathroom in the Australia area at ElectriciansForums.net
So what exactly is the circuit the FCU supplies, is it not a final circuit?We do not need to disregard Regulation 314.4 as the lighting final circuit itself complies with it as it's origin is the distribution board.
The FCU is supplied by the final circuit and itself supplies a circuit for the light and fan in the bathroom.
The reg you're referring to regarding RCD protection says that "Additional protection shall be provided for all circuits of the loacation...."
If what you're suggesting was true then surely it would say "Additional protection shall be provided for all final circuits supplying equipment in a location containing a bath or shower...." or something along those lines.
At the end of the day it's down to how each individual interprets the regulations.
So what exactly is the circuit the FCU supplies, is it not a final circuit?
Why would the wording be all final circuits? That would then allow distribution circuits to be unprotected.
In fact, it could be that the Regulation is not just for circuits that supply equipment in such locations, but also for circuits that pass through to supply equipment in other locations.
It may well be down to how an individual interprets the Regulations, although how you can interpret 314.4, and the very clear information provided in Appendix 15, in any other way than as it is written, is a mystery to me.
Of course, it may just be the case that you do not want to comply with 701.411.3.3 for whatever reason and are trying to make excuses?
Or:The reg is for all circuits of the location, not all circuits supplying the location.
I know Appendix 15 is not a Regulation, it is there to provide information in relation to the Regulations.If other circuits were passing through the location they would probably be concealed in walls or above ceilings so they would not strictly be in the location. If these circuits were installed before the requirement for RCDs then you have no obligation to bring them upto current standards as you haven't worked on these circuits.
JUD, this is becoming very tedious.
I suggest that if you can't put up then shut up.
I've answered your pointless question about Zs valus for BS1362 fuses, why won't you answer my question about what type of circuit is being supplied by the FCU?
Is it just because you know that the circuit must be a final circuit and as such is not accepted by BS7671 to be supplied from anything other than a distribution board?
A kettle meets the requirements of the definition of a circuit in Part 2, but I wouldn't call it a circuit.
I have no idea why you have stated:
Or:
I know Appendix 15 is not a Regulation, it is there to provide information in relation to the Regulations.
Should we then ignore the Tables for time/current characteristics of overcurrent protective devices in Appendix 3, the Tables for current carrying-capacities of cables in Appendix 4, the figures for voltage drop in Appendix 12, etc. as they also are not Regulations?
Or is it we just ignore the information that doesn't tally with your point of view?
JUD, this is becoming very tedious.
I suggest that if you can't put up then shut up.
I've answered your pointless question about Zs valus for BS1362 fuses, why won't you answer my question about what type of circuit is being supplied by the FCU?
Is it just because you know that the circuit must be a final circuit and as such is not accepted by BS7671 to be supplied from anything other than a distribution board?
A kettle meets the requirements of the definition of a circuit in Part 2, but I wouldn't call it a circuit.
I know Appendix 15 is not a Regulation, it is there to provide information in relation to the Regulations.
Should we then ignore the Tables for time/current characteristics of overcurrent protective devices in Appendix 3, the Tables for current carrying-capacities of cables in Appendix 4, the figures for voltage drop in Appendix 12, etc. as they also are not Regulations?
Or is it we just ignore the information that doesn't tally with your point of view?
JUD how will an RCD limit touch voltages if the fault is on a part of the circuit before the RCD?
The RCD will not detect the fault, and so will not operate.
Reply to fan in bathroom in the Australia area at ElectriciansForums.net