Forgot to add, as has been said, the strings would each have to be on there own MPP tracker but this would not bring up the 'Grid disturbance error'.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Faults on new system just installed lastweek in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
You're probably on a TNCS system which means that the installer probably should have installed an earth rod. This WON'T be the reason why your system is playing up and your installer could probably give a pretty good reason why he hasn't used one. The earth rod/no earth rod debate is still going on and I wouldn't criticise the installer for not installing one.
If the inverter has been on for more than 10 hours of feed in time it will be set now and require a grid guard code from SMA oliceman:
but I dont think this will cause tripping it must be the wiring on the A.C , if you have a 4KW system then the strings should
be 10 & 6 one in port A and other in port B .oliceman:
I had a Sunny Boy 4000tl installed last week and I have a Sunny Beam. I am getting up to 20 error records in the ERROROBJ.csv file, but cannot find out what the codes mean. I also get zero Power showing on the Sunny Beam display, usually when there is bright sun, so I am missing out on FIT. No response from the installer yet, but will keep this thread informed.
Have you done a restart on the system, full power off and back on again..Watch the inverter screen and take note of any start up messages, and make sure both strings are producing as it will switch between A & B with DC and AC values.
I had a similar problem with a 4000tl that was installed and I went out to fault find on. It had similar problems to those mentioned.
When the sun was at its peak the system did not want to play, but worked fine after 4 o'clock and before 11.30.
The first thing that I noticed was that the AC cable was 2.5mm. Whilst this is fine for a 16a radial circuit it is not right for this system. Yes, the electrician may think its right and have good reasons but this is a PV system not a heater and different rules apply. 6mm minimum!! Surely shouldbe on a 16a breaker too?
This was the first problem and was easily adressed.
The second, and something I have this place to thank for (the solution, not the problem!) was that the inverter was not set to G83. When commisioning the system the inverter should display the g83 notice on start up, if it does'nt it may not be set for the correct country. If it has been running for a while it may need a reset. The settings come at 0 and 0 and should be factory set for the country- uk, but sometimes are not. The settings for the UK are 5 and 8 on the dials A and B inside the inverter.
This sorted the problem out straight away.
Unfortunately I don't have a lot of faith in him, especially when he said it is all fairly new technology and all we electricians are still learning..but I guess looking at this forum there is some truth in that..........
QUOTE]
Sure some of us are still learning PV - but were not learning how to size cables! - Sorry i cant help with the SMA.
He assured me the 2.5mm cable is adequate for the system but I do have doubts, the cable was quite warm today when system was near max power, and now I am also wondering if he has set the country dials...
when the system re-initialises after you have turned off the dc and ac isolators it should say G83 as it is starting up. This is fairly easy to check as long as the inverter isnt tucked away in the loft! Taking the cover off is not too difficult, just an alan key but check for the g83 notice first. Yes it is new tech and we are all learning but cable sizes?
Have a look at the start up menu and write down what you see.
Reply to Faults on new system just installed lastweek in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net