Ferrule Crimps
a properly crimped bootlace ferrule, surrounds the cable and increases it’s csa slightly at the point of termination this reduces hot spots at the point of termination.
The 16A you are referring to is AWG or American wire gauge.
Took me a while to find where you were getting 14A and 16A from
Green = 100pcs Wire Range: 24A.W.G, 0.3mm2
Red = 100pcs Wire Range: 22A.W.G, 0.5mm2
Blue = 100pcs Wire Range: 20A.W.G, 0.75mm2
White = 100pcs Wire Range: 18A.W.G, 1.0mm2
Black = 100pcs Wire Range: 16A.W.G, 1.5mm2
Gray = 100pcs Wire Range: 14A.W.G, 2.5mm2
Orange = 100pcs Wire Range: 12A.W.G, 4.0mm2
Green = 100pcs Wire Range: 10A.W.G, 6.0mm2
So these are not the amp ratings. I cant find any amp ratings for them at all.
I refer you to the quote above
If you look at a reputable supplier such as Weidmuller you will see that their crimps are rated at the same current carrying capacity as the cable they are fitted to.
t
And this
you'll wonder where the yellow went, when you brush your teeth with pepsodent.
I find these on prewired 13a plugs - but where can I buy them? I need them for typical mains cables but also for 7/.02 and 16/.02 wires I use on models
Ashley-Joseph,
rynd2it,
