Fitting dol contactor for 415 v3 phase fans | on ElectriciansForums
Discuss Fitting dol contactor for 415 v3 phase fans in the Electrician Talk | All Countries area at ElectriciansForums.net
S
seadog60
I have to fit dol contactor for 415v 3phase fans where the contactor must switch at 110volt how is this done please.
when you said that it needs to swich at 110v, i thought you meant that that was your coil voltage. can you clarify what type of work your doing, and what control gear already exists?
john
I am fitting 2 new extraction 3 phase fans and on the specification the dol contactors must switch at 110v as i have not fit anything yet what would be the best way to do it
Thanks guys i shall have to have a look again at the spec as it could be that malcolm but i seemed certain it said it had to be 110v on the stop start for safety
Reply to Fitting dol contactor for 415 v3 phase fans in the Electrician Talk | All Countries area at ElectriciansForums.net
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
The 2 inputs are separate and there should be no interlinking between SL1 and2 If there is there has to be a wiring error or a fault with the...