robbie18
Does anyone have any experience of testing when generators are involved? All ZS readings come out too high for RCBO's that protect the circuits! any help or advice would be greatly received.
Discuss generators in the Electrician Talk | All Countries area at ElectriciansForums.net
to be honest i am not 100% sure on this. all i find is that when i am looking through my new companies test sheets that all zs readings are too high for RCBO's that are protecting the circuits. Are generators usually TNS earthing arrangement? Cables are run under the water so operating temperatures and everything are hard to determine. Company have the thought that if circuits are protected by RCBO's then they have done enough to which i would like clarification on.
Cables are run under the water so operating temperatures and everything are hard to determine.
In regards to an earth rod, ive just started working with generators especially tncs systems. I have found that an earth rod is used mainly as a lighting protector only and that any faults with the systems go to the star point on the transformer via the neutral. Meaning a rod is not always nessersary just like a ship as you said. Myself I would check all the earth connections and also the pen link at the genny. What is your ze at the genny? is that a normal reading
also if you know any reg numbers or other type of legistation which I could look at to educate myself more on these systems would be helpful.
Enginner54 I did not say that a earth was not required at the neutral star point of the genny. I know it is earthed to the can of the genny and then on to a ground rod. As my statment read i have just started working with generators and have been informed that on a tncs system a ground rod was not always required but i know the neuteral always is earthed to the can. Also if you look in the regs at the generator system diagram the earth line to the ground is shown as opptional per system. I do not proclam to be an expert with generators and am glad you have pulled me on these comments I was just giving my view from what i have been shown. Are you saying all normal site tncs generators need a ground rod? also if you know any reg numbers or other type of legistation which I could look at to educate myself more on these systems would be helpful.