as stated above. not my bag. i will do it though. and i will do the job well. after advice not criticism. can i not ask advice on here? so instead of being a ****? why not advise..

Honestly, from what you have said you have a very poor understanding of the job at hand, a simple job, which is why you are being asked so many questions.
Just provide as much info as possible and you will get as much help as possible. This is the internet and you can ask questions but you have no given right to receive the answers you expect to.
 
Damn thats a big mother! Sure it wont melt the plastic cups:)
Anyhow at 16mm² the armour should suffice as a CPC. So four core is a viable choice. There is a PDF on here somewhere with the steel equivalent to copper ratings. Is this clipped direct and horizontal run?
 
Last edited by a moderator:
Depending on how the adeabatic works out, existing supply test results, Zdb etc, then I would probably go with a 4 core. Use the armour as CPC, install a TPN&E socket. The N may not be required for this machine but might be needed in the future.
 
Honestly, from what you have said you have a very poor understanding of the job at hand, a simple job, which is why you are being asked so many questions.
Just provide as much info as possible and you will get as much help as possible. This is the internet and you can ask questions but you have no given right to receive the answers you expect to.
andy, as i have said, clipped direct 16mm. rather than rely on the SWA earth i would personally run 5 core? and neither to incorporate a switched fused isolator? all I'm asking
 
i haven't no. its easier to ask. but as i guessed on here its a waste of time. I'm extremely tired. earnt £1630, in 4 days and working tomorrow. but yes I'm a useless ---- yes yes. came on here for advice.
 
Steady on now, no need to get so despondent. It sounds from what you are saying it is a plan. And workable. So you have had a couple of comments but steady on now.
 
its not my bag. i just want instructions on what to do. yes i am a spark 2330 qual 10 years ago. sorry i need to ask. but i do what i do. and earn well. new job comes up ill do it ask advice. anyone want to give??
 

Reply to Glass washing machine 3 phase 63a per phase in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
353
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
320
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
368

Similar threads

Sooo the client has accepted that we don't want to be fraudulently taking electricity so that worry is out of the picture. But now basically the...
Replies
32
Views
5K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top