I believe the power 1 inverters use heatsinks and cooling fins rather than an internal fan so it would do no harm to get a large fan blowing on the inverter from early before it gets warm so to limit the heat build up. It may help. The inverter is not mounted in an enclosed space or warm loft is it?
yes its mointed in a loft bedroom, i didnt want it there as one its my daughters bedroom and two she has a pet ferret and we learned quickly that it wouldnt leave it a lone, so i had to build a ventilate box round it as well. i did bring up the t-boost issue with power one and there engernier said it wouldnt get hot enough to derate but i noticed the t-boost and temp once in may when looking at the display when it was down on peak.
this is the earlyer post i got. and it does sound the same as im getting but could be heat on panels same as mine.
Hi Billybee
I have a fairly similar system to you - Powerone PVI3000out and 13 250w suntech panels in 2 strings (these have a slightly better Temperature Coefficient than a-sun)
Have you noted the temp reading on the inverter when the power drops??
I have noted that as soon as the inverter temp reaches circa 54c the output power drops from 3300w to 2450w - the inverter display will also change from Tinv to TBoost.
Hope this Helps
Dave
i dont no why it changes from tinv to tboost at 54' and the system power drops the online manual only gives gerneral infor on it. i do think after the advice on here that even with out this at some stage on a hot day my powers going to fall by upto 20% but wonder if this is causeing reductions to happen earlyer than the panels need be. but hopefully power one will get back to me and explane more or finding a solution. the main question i had for them was if the 3.0 fell to 2450 because of this does that mean the 3600 would fall to around 2900 when the same affect happens. sadly no answer on this. i am going to get a thomitor on my roof and the next hot day i will see how hot the roof is when i stick at 2400w.
thanks again all