Just tested a home, which has three ring mains. All are 2.5mm rings with CPCs of 1.5
Both Ring 1 and Ring 2 gave normal figures for R1 and R2 however, ring 3 has a very low reading for r2 cpc.
Ring 3.
Step 1 - r1 0.56 , rn 0.61 and r2 of 0.40
Step 3 - I Checked all the sockets and had readings of betwen 0.25 and 0.28
I was expecting around 1.00 for r2 on Step 1. which would have made the readings in 3 around 0.40 (ish).
I have checked the 8 sockets that coem off it and cannot see any issues. Any thoughts on why I am getting this low reading at the CU when running continuity between E1 and E2 and when running the E1 to L2 and E2 to L1 I am getting what I should expect, based on the low cpc. so at least that matches up!!
Any help appreciated!
Thanks
Just tested a home, which has three ring mains. All are 2.5mm rings with CPCs of 1.5
Both Ring 1 and Ring 2 gave normal figures for R1 and R2 however, ring 3 has a very low reading for r2 cpc.
Ring 3.
Step 1 - r1 0.56 , rn 0.61 and r2 of 0.40
Step 3 - I Checked all the sockets and had readings of betwen 0.25 and 0.28
I was expecting around 1.00 for r2 on Step 1. which would have made the readings in 3 around 0.40 (ish).
I have checked the 8 sockets that coem off it and cannot see any issues. Any thoughts on why I am getting this low reading at the CU when running continuity between E1 and E2 and when running the E1 to L2 and E2 to L1 I am getting what I should expect, based on the low cpc. so at least that matches up!!
Any help appreciated!