Hi.

Just tested a home, which has three ring mains. All are 2.5mm rings with CPCs of 1.5

Both Ring 1 and Ring 2 gave normal figures for R1 and R2 however, ring 3 has a very low reading for r2 cpc.

Ring 3.

Step 1 - r1 0.56 , rn 0.61 and r2 of 0.40

Step 3 - I Checked all the sockets and had readings of betwen 0.25 and 0.28

I was expecting around 1.00 for r2 on Step 1. which would have made the readings in 3 around 0.40 (ish).

I have checked the 8 sockets that coem off it and cannot see any issues. Any thoughts on why I am getting this low reading at the CU when running continuity between E1 and E2 and when running the E1 to L2 and E2 to L1 I am getting what I should expect, based on the low cpc. so at least that matches up!!

Any help appreciated!

Thanks
 
Last edited by a moderator:
Sometimes readings of this nature can be found due to parallel earth paths thus reduce resistance readings, say you taken a boiler supply of the ring and the boiler has its supplimentary bonding as well as the water and gas been bonded at origin, this is just an example but shows the many paths the earth may return to the board thus reduced r2 reading, as long as you have ring continuity and no other reading abnormalities then i wouldnt scratch your head too long.

Hope this helps.
 
Darkwood - You are THE man (well for today anyway!) :)

No longer scratching my head. Forgot the spur that was running the boiler - which is connected to the main bonding probably not more than a metre or two away from it!

Thanks for that.
 
I had an extension that was added onto the ring, but they had connected all the earths into the back of the socket together.

So when testing out, the r2 reading was only being read as the original house ring.
 

Reply to Help - Problems with R2 CPC readings on Ring Main in the Business Related area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
551
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
922

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
931
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top