Nick,

There are two 32A MCBs on the consumer unit so I guess that one of those would be used for the oven. Looks like he was right when he said 2.5mm2 cable was ok! Sadly his workmanship has undermined my faith in his electrical knowledge.

Once again Nick, thanks.

you cant use a 32 amp mcb on a 2.5mm cable ,as ezziekiel has mentioned look at the manufacturer installation instruction if they do say 32 then you will need a 6 mm cable for this , what might be an idea would to contact another electrician to have a look at whats been done
 
Last edited by a moderator:
Hi Candid where about are you if your local I can pop and have a look for you, is the guy listed on the NIC list of installers?
 
Rewirable fuses look like dominos 2 coloured dots ,either white ,blue ,yellow or red , if they are MCB's the will have a number 6 a ,16 a ,20a or 32 a if they are BSEN60989 or BS3871 they will be 5a 15a 20a or 30a
and they switch on and off, not like fuses which blow and have to be replaced ( sorry nick, but i added this as the op has no electrical knowledge, as he said). personally, in my humble view, i would suggest he gets a good electrician in and has him install a 6mm dedicated cooker circuit. future proof. also. have said good electrician inspect the work so far and asvise him how to get redress via NICEIC. if we have his location,maybe he's close to one of us.
 
nickblake;201043... if they do say 32 then you will need a 6 mm cable for this[/QUOTE said:
Wouldn't 4mm be sufficiant for a 32A MCB? Haven't got my book handy so happy to be corrected.
 
and they switch on and off, not like fuses which blow and have to be replaced ( sorry nick, but i added this as the op has no electrical knowledge, as he said). personally, in my humble view, i would suggest he gets a good electrician in and has him install a 6mm dedicated cooker circuit. future proof. also. have said good electrician inspect the work so far and asvise him how to get redress via NICEIC. if we have his location,maybe he's close to one of us.

dont appologies mate its a good point i have suggested he contacts another electrician
 
Wouldn't 4mm be sufficiant for a 32A MCB? Haven't got my book handy so happy to be corrected.
4mmm may be ok, but why reun 4mmm when it's no more trouble and virtually negligible extra cost to run 6mm. better overkill than warm cable
 
how about it, candid, what's your location?
 
Wouldn't 4mm be sufficiant for a 32A MCB? Haven't got my book handy so happy to be corrected.


yes it would you are correct but im a bit old school prefer to over rate and for the length he 's doing the cost wouldnt be much differance
 
Hi mate

when you say you have 2.5mm T/E running round the kitchen from point to point this sounds like a ring for the sockets and if it is then the cooker should not be connected to this as it will increase the load excessively

if the cooker is over 2.3 kw then run a seperate supply 32A CB to a 45a double pole cooker switch with then to cooker outlet for the cooker using 6mm T/E

and yes the metal backboxes should have grommets fixed to prevent damage to the sheathing of the cable
 
Last edited:
For cooker circuits I always overate to 6mm to reason being is that I want to ensure my work will be ok for any changes that might potentially happen with any equipment being installed in the kitchen
 
Yes it a little far for me as about 50mile was thinking if was local I would have just called in whilst out and about
 
And if I take the manufacturers recommendations, what size wiring do I need? 6mm2 or 10mm2?

Also, whilst I'm on...

Under regulation 522.8.1 - 'A wiring system shall be selected and erected to avoid during installation, use or maintenance,
damage to the sheath or insulation of cables and their terminations' - are rubber grommets required for steel back boxes. There is comment on this subject on these forums but there is arguement for and against. Does anyone have a definitive answer, or this just a judgement call? At the moment the sockets aren't plastered in so I can clearly see that the grommets aren't in situ.

Thanks you all for your guidance
you wouldn't leave the screws out of a socket, so why omit the grommets. they are essential, same as you say. to protect the cable.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Help! Wiring for 4.3Kw cooker
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
52

Advert

Thread statistics

Created
candidcamel,
Last reply from
IQ Electrical,
Replies
52
Views
35,069

Advert

Back
Top