Is this part of the regulation, or just best practice?
...I may have to go to court based on this....
...I may have to go to court based on this....
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Help! Wiring for 4.3Kw cooker in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Is this part of the regulation, or just best practice?
...I may have to go to court based on this....
522.8.1, and 522.8.11 (sharp edges)
i assume cooker is on own circuit as they say over 3kw , should be .
4300w/230v= 18.6A , should be ok .
2.5mm t&e cable can take 27A clipped direct.. if has going through walls and ambient is high could be different.....
Reply to Help! Wiring for 4.3Kw cooker in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net