Hi I was wondering if any one can help me. I've done a R1 and R2 reading on a lighting circuit and there is a high reading in the middle of the circuit. I would usually expect the highest reading at the end of line. Does any one know why this is happening thanks
 
Yeah all tight, it's part of a consumer unit change and done in 1mm but after the high reading there is a 1.5mm to the next light fitting as there was a fault before would this have an impact
 
Just because they are tight doesn't mean there is a good connection, there could be insulation in the way or a damaged conductor. If nothing is visible then you need to get your tester out and break the circuit down until you find out where the problem arises.
 
how much higher? if the light with the higfh reading is 2 way or 3 way switching, you'll be reading the strappers as well.
 
It's not much higher about 0.30ohms higher it's just on a 1 way light it has thrown me tho as it then drops down again. I know it's in the middle as I've worked out the path of cable as I had to find a fault
 
I've tested at every point to check there's an earth at each point, but the light point in middle was the highest then dropped down again
 

Reply to High R1 & R2 reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
701
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
805
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top