TheCodboy

-
Arms
Joined
Dec 20, 2012
Messages
371
Reaction score
128
Location
Newcastle
Hi all, Doing some pre board change testing and ive found 2 sockets with high Zs readings. Everything else is fine, done all my end to ends and the Zs's are what should be expected. A couple of the sockets have Zs lower than expected but 2 are higher. They should be about 0.8 ohms but ive got one at 1.20 and one at 1.40. Taken the highest value socket off, re terminated, still high. Tested at the terminals of the socket just in case the socket was duff, but still high. Its a PME system with a good low ZE (0.15). Any thoughts people??
 
Hi all, Doing some pre board change testing and ive found 2 sockets with high Zs readings. Everything else is fine, done all my end to ends and the Zs's are what should be expected. A couple of the sockets have Zs lower than expected but 2 are higher. They should be about 0.8 ohms but ive got one at 1.20 and one at 1.40. Taken the highest value socket off, re terminated, still high. Tested at the terminals of the socket just in case the socket was duff, but still high. Its a PME system with a good low ZE (0.15). Any thoughts people??
Are the sockets in question spurs?
 
I had a job this week, where I removed some diy work on what I thought was an RFC in an existing extension. Well I thought it was an RFC, but in fact it was fed via a spur from another RFC.
 
how many cables was at this socket ? you posted you had done end to end at consumer unit (assumed) what about r1 + r2
The socket with the highest reading had 2 x 2.5 T&E. Took L-L, N-N, E-E reading at the consumer unit. r1 + r2/4 + Ze = 0.82 Ze was measured at 0.14. The calculated Zs of 0.82 was very near what i was getting all around the ring. 2 sockets were a bit lower (0.45 & 0.55) and apart from the 2 that were high, the rest were virtually spot on. ( My end to end values were L=0.92 N=0.92 E=1.83)
 

Reply to High Zs value with 2 sockets in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
344
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
882
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top