C

chris-

hi people,
How/ why am i supposed to bond the main water when it comes into the house in plastic. i thought it would be a deviation but ive now been told by a guy who said that the niceic said to bond the plastic pipe as the power supliers recomend it.
 
Did Nic guy mean to say

If the incoming service pipes are made of plastic, they
do not need to be main bonded.
If the incoming pipes are made of plastic, but the
pipes within the electrical installation are made of
metal, the main bonding must be carried out. The
bonding being applied on the customer side of any
meter, main stopcock or insulating insert and of
course to the metal pipes of the installation.
 
Last edited:
Ive always bonded all exposed plastic in the houses I've worked in, doors, window frames, cat flaps, shower trays, Tv's toothbrushes the lot....are you telling me I've been wasting my time all these years?


You have done well mate!

A few more like you and our profession could be classed as professionals!!

Any ways, some on here may say you may have gone a little overboard, but I wouldn't listen to them.

You stick to your guns. well done mate!!!
 
I agree with des 56 as you have metal pipe work in the dwelling it has to be bonded back to the met or main earth in the ccu other wise under fault conditions that pipe going to go 230v and that stings . you have water pumps ,emersion heaters ect that can fail and will make that metal work live ,no bond no fault path idealy you need a reading of 0.05 ohms or below to achieve this on the metal work.i have been to a job where there was a reading on the radiatorof of 238v discoverd plumber had nicked the cable and it was touching the pipe work and it energised the pipe work ,
 
Last edited:
I know we can all see the funny side of this post but that is another guy that will probably never post again. Out of 17 replies only 2 gave constructive advice!

How can an electrician post such post as the OP?

How can he be an electrician and not know that plastic pipe does not conduct?

The OP has no business of doing such critical work, when he has no understanding of what he is supposed to accomplish?

He is non-electrician and an imposter.
 
I find 100mm is too short,

I normally cut 102mm of the plastic pipe and fit 100mm of copper in place.
So you're a time served plumber then? :lol:

- - - Updated - - -

I understood that the B*gg*r word and other such words were not allowed by this forum?????
They're not, I misspelled bigger.
 
How can an electrician post such post as the OP?

How can he be an electrician and not know that plastic pipe does not conduct?

The OP has no business of doing such critical work, when he has no understanding of what he is supposed to accomplish?

He is non-electrician and an imposter.
He doesn't claim to be a full spark. He could be doing onsite work in his first year as an apprentice (admittedly it would have to be near the end of his first year).
 
I know we can all see the funny side of this post but that is another guy that will probably never post again. Out of 17 replies only 2 gave constructive advice!
I see where you're coming from however even I know the answer to this one so that says a lot about the OP.
 
How can an electrician post such post as the OP?

How can he be an electrician and not know that plastic pipe does not conduct?

The OP has no business of doing such critical work, when he has no understanding of what he is supposed to accomplish?

He is non-electrician and an imposter.

That was obvious after reading the OP to most people surely!
 

Reply to how am i supposed to bond the main water when it comes into the house in plastic in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
787
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
241
I am living in the north of Thailand outside of the big city. That means in the rainy season we have multiple times per week power outages...
Replies
0
Views
454

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top