How would you go about changing this unit over?

[ElectriciansForums.net] How would you change this.


Old wylex board with Pyro mains tails. Earthed via Pyro, and all circuits via conduit.

Protrudes out the wall so I was thinking 1 of options, as I can’t see any other way round it.


Option 1
Batten on each side of the DB to the same level of the current one, crimp all cables and mount new unit over the old one.
Take a 16mm cpc from old board to new board.

Option 2
Angle grind the DB so it’s level with the wall and do same as above.

Option 3
Remove current DB completely and try to get another one in the same space, attempt to alter conduits and pyro to fit.
Don’t fancy bending pyro!
 

Attachments

  • [ElectriciansForums.net] How would you change this.
    07D8528B-7DCC-4217-B602-892FD75F2449.jpeg
    321.1 KB · Views: 95
  • [ElectriciansForums.net] How would you change this.
    CEE0A6FF-92CF-40FF-A0DB-39BF30776208.jpeg
    380.5 KB · Views: 96
You could get another one in, would need to dig the wall out quite a lot though. Id use a Hager board, the model with no knockouts.

I've seen people fit new boards on top of old ones, but I've never seen that done in a way I'd consider satisfactory. Those conduits are probably 3/4 inch.

Edit I've just seen the conduits are at the bottom and top of the enclosure, I'd probably cheat in that case, cut the enclosure flush with the wall then mount a new cu on top. Not ideal but there is little else you can do without digging the conduits right out of the wall to adjust them to the new cu height.
 
How would you go about changing this unit over?

View attachment 64229

Old wylex board with Pyro mains tails. Earthed via Pyro, and all circuits via conduit.

Protrudes out the wall so I was thinking 1 of options, as I can’t see any other way round it.


Option 1
Batten on each side of the DB to the same level of the current one, crimp all cables and mount new unit over the old one.
Take a 16mm cpc from old board to new board.

Option 2
Angle grind the DB so it’s level with the wall and do same as above.

Option 3
Remove current DB completely and try to get another one in the same space, attempt to alter conduits and pyro to fit.
Don’t fancy bending pyro!
Option 2
 
Unless you start talking rewire, it's adapt the existing box with the conduit entries.
I'd be checking the load and size...that pyro term looks a bit sweaty.
Is it a flat?
Interesting for a domestic job. Quite costly for a board change.
 
Cheers guys, I had already opted for option 2 if I get it, I just always wonder what other people would do in these situations.
It’s not ideal, but the only way round it really without a rewire.

If I end up doing it I’ll post up pictures!

Its a tiny ex-council studio flat, with a 60a isolator, load isn’t an issue for what’s currently in there.
 
Remove the guts, fit a din rail on standoffs with standard main switch and compact RCBOS, mount a neutral bar in the back of the enclosure on insulated standoffs. Make a nice cover out of polished brass plate a little larger than the box, bevel the edges of the plate for decoration. Drill fixing holes to match the existing lid lugs and cut out a rectangle for the devices to poke through. make a hinged cover to go over circuit breakers, formed again from brass plate, this time shaped with an industrial press. Fit lid to enclosure using copper or brass dome head rivets. Etch the brass with circuit information, filling the etched parts with dark blue enamel paint. Polish and fit cover with new brass pan head machine screws.
 
Cheers guys, I had already opted for option 2 if I get it, I just always wonder what other people would do in these situations.
It’s not ideal, but the only way round it really without a rewire.

If I end up doing it I’ll post up pictures!

Its a tiny ex-council studio flat, with a 60a isolator, load isn’t an issue for what’s currently in there.
Good choice,& yes a rewire would be better,& a recommendation to the client.
 
Unless the board change was part of a full rewire I personally would not entertain it.
i have come across them where the electrician butcher / mount a new plastic board over the top and try to extend the old wires using crimps and connector block etc but look dog rough With loads of mastic and no nails holding them on.
 
Cheers guys, I had already opted for option 2 if I get it, I just always wonder what other people would do in these situations.
It’s not ideal, but the only way round it really without a rewire.

If I end up doing it I’ll post up pictures!

Its a tiny ex-council studio flat, with a 60a isolator, load isn’t an issue for what’s currently in there.
You cannot grind a CU down as you suggest. You are now the designer if anything should happen.

I'd price to do the job properly or not at all. Either way its not the usual (for here) ÂŁ200 CU swap.
 

Reply to How would you change this. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
717
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
  • Question
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top