Hi just joined and was reading thread, i was told once that immersion should'nt be on plug top as our 13amp plugs are not actually rated at 13amps only rated at 9 amps for periods of long use.
After two attempts to get the NICEIC Technical to answer my questions in written e-mail format I received two answers many days after, the first answer was not a direct answer to my question, but the second answer was.
Answer one - In answer to your question regulation 554.3.3 does clearly state connection by double pole linked switch without use of plug and socket, also appendix 15 does state loads over 2KW should be on their own dedicated circuit.
Answer two - I do not believe that this section refers to standard domestic immersion heater elements that are considered to have insulated elements.
GN 1 does confuse matters somewhat in determining that immersion heaters (in general) should be on their own circuit and then refer to section 554.3
In future I will be better off asking people like IQ & Wirepuller any Technical Questions, because the NICEIC inbox was not very full shall I say when I asked the questions in the first instance.
So what really ----es me off is, they send out one of their inspectors every year to assess me and the company I work for and really try and be clever with their attitude, and say your wrong on this and that, then their Technical back up don't really like to back up their inspectors.
Told my mate to leave them and join another scheme, but he won't lol
Well at least the NICEIC have been able to clear that up.
What was the question again?
What comes first the chicken or the egg............................................. hehe
After two attempts to get the NICEIC Technical to answer my questions in written e-mail format I received two answers many days after, the first answer was not a direct answer to my question, but the second answer was.
Answer one - In answer to your question regulation 554.3.3 does clearly state connection by double pole linked switch without use of plug and socket, also appendix 15 does state loads over 2KW should be on their own dedicated circuit.
Answer two - I do not believe that this section refers to standard domestic immersion heater elements that are considered to have insulated elements.
GN 1 does confuse matters somewhat in determining that immersion heaters (in general) should be on their own circuit and then refer to section 554.3
In future I will be better off asking people like IQ & Wirepuller any Technical Questions, because the NICEIC inbox was not very full shall I say when I asked the questions in the first instance.
So what really ----es me off is, they send out one of their inspectors every year to assess me and the company I work for and really try and be clever with their attitude, and say your wrong on this and that, then their Technical back up don't really like to back up their inspectors.
Told my mate to leave them and join another scheme, but he won't lol
MK Control Switch 20A DP 1 Gang + Neon + Base by MKThanks Tony. I have to admit I was at cross swords with Tony on this and thought that a domestic immersion was indeed under regulations 544.3.3, but it would appear not. So thank you for seeing this through.
Though there would not be a contravention of the Regs by fitting this to a BS 1363 socket and plug, how many of us would actually do the installation this way, I don't think I would be one to use this method as my first choice.
We now have through this thread comments that by fitting it on a 13amp FCU should be discouraged because a 3KW appliance at 230 volt takes over 13amps and at certain temperature ranges this could affect the integrity of that FCU, then surely this would be the same for a 13amp plug top and socket.
It seems the only fool safe method is a 16amp Radial circuit supplying a 20amp double pole switch. Though this method would entail a certain amount of difficulty terminating the flexible cable from the heater into the switch, as unlike a FCU that as the flex outlet capacity I can't think of a switch that as this capability.
Successfully drained tank & removed old immersion - cleaned threads on tank - good as new.
what code would you give for immersion with shower pump on same circuit?