QUOTE what about bonding?

Where do you find a bare resistance wire in water?

Where then are the regs for the connection of domestic immersion heaters?
QUOTE


Bonding is at the point of entry...a metallic pipe does not have to be continuous beyond the point of bonding.

I've never come across bare resistance wire in water,but then I've never come across bare electrodes in water and yet there are a set of regulations for those.

There are no specific regulations for the connection of domestic immersion heaters because general regulations apply. There are specific regulations for electrode and uninsulated elements because of the additional hazards associated with them which are not present with a normal insulated element.

Well thats my interpretation anyway!
 
Last edited by a moderator:
Don't bare electrodes/elements do their job in insulated Tanks ?

Just answered the question myself I think lol

Bare element = class 2 insulated tank

Insulated element = class 1 metallic tank
 
Last edited by a moderator:
There are no specific regulations for the connection of domestic immersion heaters because general regulations apply. There are specific regulations for electrode and uninsulated elements because of the additional hazards associated with them which are not present with a normal insulated element.

Well thats my interpretation anyway!


Guidance Note 1 (Selection and Erection)
page 131 C5 WATER HEATING AND ELECTRIC SHOWER FINAL CIRCUITS
says that domestic immersion heaters should not be connected by a plug and socket outlet and the reg it refers to is 554.3.3!!!

OSG app 8 (standard circuit arrangements for household and similar installations) 8.5 WATER AND SPACE HEATING - immersion heaters should be connected by outlets complying with BS 1363-4

Where are these immersion heaters in domestic situations if not in our large copper hot water tanks :p:)
 
In my previous post about the construction of an domestic immersion heater, I obviously didn't make myself clear, so hopefully the following will.

First an apology:
Sorry, I did not have my Regs book at hand (left it at work) and quoted the wrong Reg Number used elsewhere in our discussion thread so please ignore that and refer to my correction below.

The actual element of resistance wire is insulated from the earthed protective tube. If the insulator is air then the element will be wound on a former with regularly spaced supports, to prevent shorting to the tube. If on the other hand the insulating material is silica (refined sand in effect) the element can be a self supporting spiral of wire held under tension, the silica is then added under pressure to preventing shorting to the tube, the tube is then capped to prevent the loss of silica and then bent into a loop ready for fixing to the header.

A domestic immersion heater is an insulated element and therefore 554.3 does not apply.
The 554.3 group of regulations apply to instantaneous water heaters eg. showers and quick-boil heaters etc.

Correction:
Electrode boilers are covered by 554.1 group of regulations.

Once again sorry for any unintentional confusion caused.
 
Mark - So your of the same opinion that the heater element is of an insulated type ?

When the NICEIC get back to me by e-mail, if their response goes against what the retired engineer said/the Technical guy yesterday, it will be slightly embarrassing to say least, for them and me.

I've got work today so won't know any response until I get in later.
 
Guidance Note 1 (Selection and Erection)
page 131 C5 WATER HEATING AND ELECTRIC SHOWER FINAL CIRCUITS
says that domestic immersion heaters should not be connected by a plug and socket outlet and the reg it refers to is 554.3.3!!!

OSG app 8 (standard circuit arrangements for household and similar installations) 8.5 WATER AND SPACE HEATING - immersion heaters should be connected by outlets complying with BS 1363-4

Where are these immersion heaters in domestic situations if not in our large copper hot water tanks :p:)

Pushrod you may well be correct and I'll put my hands up if you are...GN 1 is in the office and I will check out your reference later.
The sticking point for me is 554.3.2 I do not see how this can be applied to a normal domestic immersion heater,in fact it cant....it is that and that alone which makes me think that 554.3 does not refer to a type of heating element I am familiar with.
 
[ElectriciansForums.net] immersion heater and a shower pump
[ElectriciansForums.net] immersion heater and a shower pump Exposed element.
 
yeah you can see the coiled resistance wire encased in an insulator like magnesium oxide or something similar. It would be inconceivable to ever have a design where it was just flopping around inside the metal casing. It is the same with cooker elements.
 
Stop Press: Immersion element construction update.
I've been in contact with half dozen leading manufacturers of domestic and industrial immersion elements this morning.
It appears air insulated elements are 'old school' and rarely manufactured today and silica insulated elements are reserved for the budget end of the domestic market.
In order to achieve higher wattage densities, thermal efficiency, maximum electrical insulation, hot spot reduction and long life the insulation material most manufacturers currently use is compacted refractory magnesium oxide (MgO) in both domestic and industrial immersion heaters.
Summary:
Electrical manufacturers confirm domestic immersion elements are of insulated construction and that the 554.3 group of regulations do not apply to their products. Heatrae Sadia and Santon going further, stating that the 554.3 applies specifically to shower and quick-boil instantaneous water heaters.
 
Last edited by a moderator:
Mark

Thanks for your input.

Update from me

Still no e-mail from the NICEIC. But I got my QS yearly assessment dated 2007. Amongst it was a periodic which included a code for an immersion heater on plug top.

Now normally when you do something what does not comply with BS7671 the NICEIC Engineer notes the issue and put a cross in a box to show you never complied and offers an explanation as to why.

Now this sheet stated immersion heater on plug top does not warrant a code, now its looks like a number after the code, but can't fully make it out. But the regulation number quoted was in the 744 range. So it might of been the case where the immersion heater was in a airing cupboard which was in a bathroom.

But normally when the NICEIC Engineer believes a coding is warranted but you got the coding wrong they would offer a different coding, but in this instance he never.

Will update when I know more.
 
Checked GN1 today and Pushrod is correct as it clearly states household immersion heaters should not be on a plug and socket and refers to reg 554.3.
However this gives the impression that regs 554.3 (immersed uninsulated elements) includes normal domestic elements.
This is at odds with the requirement of reg 554.3 which states that the elements referred to must comply with 554.3.2.
554.3.2 states that all metallic parts of the water heater except current carrying parts must be solidly connected to a metallic water supply pipe,and that water supply pipe must be earthed back to the MET by means independant of the circuit CPC.
A normal domestic imm heater is fed by a copper pipe from a plastic header tank,that pipe is not normally connected to the MET,does this mean that the majority of domestic water heaters dont comply?....no,I still believe 554.3 does not apply to domestic insulated elements and possibly GN1 is not referring to the correct regulation.
 
Wirepuller

When I used to quote guides etc to our Engineer, his answer was not interested in them, your working to BS7671 and that's what me and you refer to.

Guides are just that.
 
554.3.2 states that all metallic parts of the water heater except current carrying parts must be solidly connected to a metallic water supply pipe,and that water supply pipe must be earthed back to the MET by means independant of the circuit CPC.
A normal domestic imm heater is fed by a copper pipe from a plastic header tank,that pipe is not normally connected to the MET,does this mean that the majority of domestic water heaters dont comply?....no,I still believe 554.3 does not apply to domestic insulated elements and possibly GN1 is not referring to the correct regulation.

I take your point that there seems to a discrepancy here. My own feeling is that it(reg 554.3.2) dates back to pre 17th where you would expect there to be supplementary bonding on the pipe work and that it has not been updated to go with the fact that installations to the 17th edition, with circuits under the control of RCDs, no longer require supplementary bonding to metallic boiler pipework. ??

If not i still ask where are the immersion heaters that these regs apply to?

Also, i think "uninsulated element" is not referring to the resistance wire not having insulation around it, but to the fact that there is no insulation around the outer metal case of the heating element.

It would be interesting to get a few more opinions, maybe someone like widdler or IQ.
 
Wirepuller

When I used to quote guides etc to our Engineer, his answer was not interested in them, your working to BS7671 and that's what me and you refer to.

Guides are just that.


But the OSG and the Guidance Notes are all written by the same people - the IEE - to help explain BS7671, strikes me as a bit of an arrogant attitude by the engineer.
 

Reply to immersion heater and a shower pump in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
591
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Every oil boiler I've worked on has used a photocell for flame detection. Even though your boiler is inefficient by current standards, as long as...
Replies
4
Views
421
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top