Post #1 suggests differently.lol!! ...Enough said then!! Your problem, ...not mine!!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Interested in your thoughts.... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Post #1 suggests differently.lol!! ...Enough said then!! Your problem, ...not mine!!
Post #1 suggests differently.
BTW E54, I did not post my conclusions, because I would have come up basically with your points, obviously bar the knowledge of the actual specs of the job.
A lollipop is "acceptable" but confusing.
I would not install one on a new install, but, I would be tempted to mod an install to one, if cost was a significant factor.
BTW why rings not radials?
Is it a load distribution/volt drop thing?
If so you had better ensure that the rings are wired "every other" as it were!
Your thread, your problem.Explain yourself then, ...cause everyone loves a smart arse!!
Your thread, your problem.
I was only trying to help by contributing to it, eg suggesting you shouldn't reduce the csa of a cable over 3m without a protective device, as per BS7671.
Sorry if that came across as being "smart".
I think you would need to identify if the 6mm "lollipop" was a sub main or part of the RFC
543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the conductors of the ring, the circuit protective conductor of every ring final circuit shall also be run in the form of a ring having both ends connected to the earthing terminal at the origin of the circuit.
So I suppose mate that if the ring starts at the junction box it would comply, but if the RFC starts at the CU then it does not comply.
Bottom line as you say mate it is just really not a good way to have a circuit IMO
I suppose by the letter of the regs you should as your reduction in CSA will exceed 3 metres, but has the protection is just 32amps for the entire circuit and your using 6mm radial and 4mm for the RFC then I would only be fitting the one OPD at the origin.
Reg 434.2.1 IMO is aimed a circuit where you have a 63amp Ring Main in 10mm and you want to tap off for <3 metre in say a 6mm for something.
Well you have 2 options:
It's up to you which one you choose, but I would go for the second option.
- Wire the cct as a FLC
- Do it properly.
That's my thought on the matter, take it or leave it.
IMO it relates more commonly to the reduction in CSA of a pendant wired in 0.5mm flex from a 1mm or 1.5mm lighting circuit, but either way in this situation there should be a protective device at the reduction in CSA where the ring 'lollypops' off, making the SWA a submain. The ring would then begin at this point, in line with convention.I suppose by the letter of the regs you should as your reduction in CSA will exceed 3 metres, but has the protection is just 32amps for the entire circuit and your using 6mm radial and 4mm for the RFC then I would only be fitting the one OPD at the origin.
Reg 434.2.1 IMO is aimed a circuit where you have a 63amp Ring Main in 10mm and you want to tap off for <3 metre in say a 6mm for something.
Read what you entitled the thread.Read post #25!!!
Funnily enough, I really don't need you telling me how to ''Do it properly''.