this thread will go on for quite a while (14 WEEKS), to exams... ive nearly read gn3 for the first time and there is a few things i dont fully understand but im sure i will for when the time comes from help from you guys/dudes/punks who know just a little to much.
 
alright lets do this..

The maximum tabulated values of earth loop impedance, given in BS7671, for three circuits are 2.3Ohms, 1.44Ohms and 0.57Ohms.
The measured values for these circuits are 1.22Ohms, 0.44Ohms and 0.36Ohms respectively. Determine if the measured values are acceptable.
Show all calculations.
 
An RCD to BS EN 61008 is to provide additional protection for a 13a socket-outlets, for use by an ordinary persons, intended for general use. State
a)the maximum permitted operating current (I∆n) of the RCD
b)the maximum test current when testing a device in a)
c)the maximum permitted disconnection time for test in b).
 
2.3 ohms x 0.8= 1.84 0hms ,1.22 is acceptable
1.44ohms x0.8= 1.15 ohms, 0.44 ohms is acceptable
0.57 ohms x 0.8=0.45 ohms,0.36 ohms is acceptable
alright lets do this..

The maximum tabulated values of earth loop impedance, given in BS7671, for three circuits are 2.3Ohms, 1.44Ohms and 0.57Ohms.
The measured values for these circuits are 1.22Ohms, 0.44Ohms and 0.36Ohms respectively. Determine if the measured values are acceptable.
Show all calculations.
 
a, 30mA
b,150mA
c,40ms

An RCD to BS EN 61008 is to provide additional protection for a 13a socket-outlets, for use by an ordinary persons, intended for general use. State
a)the maximum permitted operating current (I∆n) of the RCD
b)the maximum test current when testing a device in a)
c)the maximum permitted disconnection time for test in b).
 
right ok.. last one for an hour coz the mrs is makin me sit thru the only way is essex... :90: god i hate that show.

The perspective fault current at the origin of a 230v single phase installation forming part of a TN-S system is to be measured. State
a) the conductors between which testing is to be carried out
b) which result from a) is to be recorded on an Electrical Installation Condition Report
 
in a bathroom does your raidator have have to be connected to the lighting circuit in bathroom??? or is that old practices..

i thought if you have main protective bonding in place , it eradicates all this supplemntry bonding /equopential bonding
 
name the protective conductive that connects the following;

exposed conductive parts to extraneous conductive parts where a circuit discconnecion times cannot be met

awnser; supplementry bonding conductor


is that right something telling me equapotential bondonding conductors or is that the same as supplementry
 
in a bathroom does your raidator have have to be connected to the lighting circuit in bathroom??? or is that old practices..

i thought if you have main protective bonding in place , it eradicates all this supplemntry bonding /equopential bonding
older installations that dont have RCD protection will/should have supplementary bonding between exposed and extrainious parts.......the use of RCDs does away with this arangement....but if working on an older install where theres no additional protection by means of RCD...and supplementary bonding isn`t in place.....then both the circuit feeding the bathroom (special location) and the absence of supplementary bonding within special location becomes a "2"......
 
Last edited by a moderator:
you wouldnt have that diagram on earthing and protective conductors from the red wiring regs on your computer or where i can find it.. dont have red book anymore or what the parts in question are

they labelled M, C, P
 
Last edited:

Reply to just started the 2391 in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
800

Similar threads

  • Question
My older card has it but my newer card doesn’t
    • Like
Replies
1
Views
723
  • Question
yeah, think this will be the best way around it for me, thanks, having thought about it, if the country is as short of sparkys as peope make it...
Replies
3
Views
624

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top