now i understand if 30mA rcd is used you get 1666 ohms , now what happens if was no rcd what value for Ia would you use.., say was a bathroom with 40A shower R= 50/200=0.25 ohms, 6A lighting circuit R=50/30=1.7 , a radiator and towel rail
and a hotpress with copper heating tank
so does all the circuits need to be bonded together..
so R must be less than 0.25 ohms and all extraneous / exposed conductive parts must be connected to the CPCs of the circuits involved.
i know if main protective bonding is in place you dont need all this... just put me straight