For TT surely there must be some kind of RCD up front, as changing to SWA would be worse than useless - a nail connecting to a live wire and to a high Z earth that just makes the building live but trips nothing is worse than a nail on its own that is just live.
If you can beef up the thin bit of wall to 50mm, or maybe make the route un-hidden in some way (metal detector and some labels/paint ? ) then a 100mA or 300mA up front would be my preferred But a long run of any cable on TT without an upfront RCD is asking for trouble, even a few m of meter tail in plastic trunking feels icky.
 
For TT surely there must be some kind of RCD up front, as changing to SWA would be worse than useless - a nail connecting to a live wire and to a high Z earth that just makes the building live but trips nothing is worse than a nail on its own that is just live.
If you can beef up the thin bit of wall to 50mm, or maybe make the route un-hidden in some way (metal detector and some labels/paint ? ) then a 100mA or 300mA up front would be my preferred But a long run of any cable on TT without an upfront RCD is asking for trouble, even a few m of meter tail in plastic trunking feels icky.

An upfront RCD is not a must, although in most TT situations tt is highly likely. Especially in domestic situations where it is not only needed for fault protection due to low Zs.

I've done a few installations where the Ra is sufficient not to require them.
 

Reply to Landlords EICR and t&e sub mains without RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
309
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top