For TT surely there must be some kind of RCD up front, as changing to SWA would be worse than useless - a nail connecting to a live wire and to a high Z earth that just makes the building live but trips nothing is worse than a nail on its own that is just live.
If you can beef up the thin bit of wall to 50mm, or maybe make the route un-hidden in some way (metal detector and some labels/paint ? ) then a 100mA or 300mA up front would be my preferred But a long run of any cable on TT without an upfront RCD is asking for trouble, even a few m of meter tail in plastic trunking feels icky.
If you can beef up the thin bit of wall to 50mm, or maybe make the route un-hidden in some way (metal detector and some labels/paint ? ) then a 100mA or 300mA up front would be my preferred But a long run of any cable on TT without an upfront RCD is asking for trouble, even a few m of meter tail in plastic trunking feels icky.