Landlords EICR and t&e sub mains without RCD | Page 3 | on ElectriciansForums
Discuss Landlords EICR and t&e sub mains without RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
For me right now .
Both.
But I'm willing to be persuaded otherwise .. but I'm not yet.
If you need RCDs for basic protection you are in a whole world of trouble and cables in walls is the least of your worries.
Do you know that the T&E is buried at a depth of less than 50mm?
Maybe you can see that it is, or maybe you're guessing?
I had a similar situation recently. As far as I could see it looked like the cable was always over 50mm deep in the wall, but I couldn't inspect the whole run.
I didn't code it, but listed it in the limitations. You'd hope that the people who installed it 5 years ago would've done it properly...
With tt anyhow
With tncs or tns yes its additional... but it's still a requirement really unless someone can show me something that says different.
It is a requirement. So is brown sleeving on black cables that are live. Does not make it potentially dangerous if it is missing though does it.
Just thinking out loud - if the TT was PME’d then at least the sub-main would have fault protection. I did a job recently where SSE had just been through and upgraded the o/h and were able to provide PME.
Would there be much point putting a 100ma RCD upfront of one of these sub mains as it still wouldnt meet the 30ma requirement?
in my opinion it would be worth it, especially if it was me that had just put a nail through the cable.
Reply to Landlords EICR and t&e sub mains without RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...