Landlords EICR and t&e sub mains without RCD | Page 2 | on ElectriciansForums

Discuss Landlords EICR and t&e sub mains without RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

That won’t comply. Cables buried in walls need to have 30mA additional protection.
Oops, I forgot this was also a problem to be solved. If they’ve put the unprotected sub main in a wall less than 50mm then my 100mA S type is no good .
 
Personally I think the cost to install SWA or surface cabling is too high when compared to the safety improvement. If I was the landlord I would not bother installing additional RCD protection for cables in walls in these properties and ensure S Type 100mA RCDs were installed for all sub-distribution circuits on TT supplies.
 
Eerr
You can see a socket ....
You can't see a buried cable..
You can screw into the live then lick the screw ... if your that way inclined..
No operation of any protective device..
Is this not the point..?
 
Eerr
You can see a socket ....
You can't see a buried cable..
You can screw into the live then lick the screw ... if your that way inclined..
No operation of any protective device..
Is this not the point..?

It's sort of the point, if your point was that you cannot possibly protect against every random eventuality and so coding should be realistic based on normal use of the installation. But I don't think that was your intended point, just what I inferred from that.
 
It's sort of the point, if your point was that you cannot possibly protect against every random eventuality and so coding should be realistic based on normal use of the installation. But I don't think that was your intended point, just what I inferred from that.
Why do we fit RCDs for stuff buried in a wall less than 50mm deep if not to guard against things that aren't "normal use"??
 
Because if I am the inspector I am suitably competent, qualified and experienced enough to judge a T&E ‘sub main’ as was described in the original OP as a C3 :)
Ok I accept that point of view.
This is why Im Posting this .. because I value the feedback here.
At this time I'm not completely sure i agree completely.
The thing that worries me is just that we have the current regs for a reason .. this goes against them.
I need to be happy with what I'm doing .. so I seek consensus...not just cost cutting for landlords.
I thank you for your points.
 

Reply to Landlords EICR and t&e sub mains without RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
308
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top