That's the trouble I have. It seems to comply with the standard (so long as the instructions are good enough to meet the lab's interpretation of the cl4 requirement "minimizes the risk of danger to the user or the surroundings") but I don't know the law/regulations well enough to say if this would fall illegal under the EHSRs on its own. I can check the LVD, but don't know if there is anything similar in the Part P or or other regs that would forbid this arrangement. [edit: sorry, you do clearly state the EHSRs require the product to be safe - - if there any laws other than the LVD/LV Safety Regs/plug and socket regs, could you point me to them please?)The law is not as specific as to give the level of detail you seek.
The EHSR’s of the law merely require the product to be safe.
A BS is not law and is not mandatory.
However deviations from a BS would mean that the manufacturers would have to be able to justify the same or greater safety than afforded by following the relevant BS product standards.
(much simplified explanation)
That's the trouble I have. It seems to comply with the standard (so long as the instructions are good enough to meet the lab's interpretation of the cl4 requirement "minimizes the risk of danger to the user or the surroundings") but I don't know the law/regulations well enough to say if this would fall illegal under the EHSRs on its own. I can check the LVD, but don't know if there is anything similar in the Part P or or other regs that would forbid this arrangement.
Plugs and sockets outlets are excluded from the LVD, because the standards to which they are made are national, not harmonised. I am not sure (but we should probably find out) how the LVD applies to a socket outlet with integral electronics, such that the electronics lie within the scope of the LVD. There is this: Announcement: server inaccessibility - European Commission - http://ec.europa.eu/DocsRoom/documents/20341 but I can't access it at the moment because the Europa site is down. It might only concern plug-in devices, I can't recall.
Part P doesn't care a jot how the terminals on a socket outlet are arranged. It is a building regulation that obliges installers to comply with BS7671 in order to also comply with building regs, and to notify and certify certain works. It does not apply at all in many locations. BS7671 does not itself explicitly require socket outlets to be made to BS1363, however any alternative would be expected to achieve the same level of safety and it would be an uphill struggle to demonstrate how a socket not made in compliance with that standard would do so, in a UK domestic environment.
Who has a copy (or sight of a copy) of BS1363?
With my regulatory hat on ........
The UK 'law' on plugs and sockets is implemented through Statutory Instrument 1768, "The Plugs and Sockets etc. (Safety) Regulations"
This specifically requires socket outlets to comply with BS1363-2 plus amendments.The Plugs and Sockets etc. (Safety) Regulations 1994
These Regulations re–enact with modifications the provisions of the Plugs and Sockets etc. (Safety) Regulations 1987 (S.I. 1987/603) and make provision for the first time for certain requirements to be satisfied in relation to appliances.www.legislation.gov.uk
The standard defines not only construction requirements but also the plethora of tests that must pass for the design to be approved.
It requires products to be tested and approved (type testing) by an accredited test house, to the standard, before they are put on the market, and requires marking on the product to identify the test house to show compliance.
It is not permitted to CE mark plugs and sockets (now going to be UKCA since Brexit), 'self declaration' is not allowed for plugs and sockets, so the only legitimate route to market is through notified body testing.
The Socket under discussion has a spurious CE mark. I didn't see the mark of an accredited test house anywhere, and as Lucien commented on the 'instructions', I don't think any test house would have passed the instruction leaflet anyway.
I don't believe there is anything specific in BS1363-2 to say that multiple earth terminals must be connected (I could be wrong), so that doesn't help the cause, but it is plain that supplying these things is against regulations, so I believe Trading Standards could take action.
As I understand it only Standard Plugs need Notified body approval (Regulation 8) but Sockets fall under "Regulation 10 Electrical devices other than standard plugs" which only require testing. Agreed re: BS 1363-2, though, I can't find anything specific in that states that the earths must be linked, but the General requirement in cl.4 states that risks must be minimised so it is down to the lab interpretation of what this means. CE would still be needed if there is a CE Function like WiFi under Radio Equipment Directive/Regulations.With my regulatory hat on ........
The UK 'law' on plugs and sockets is implemented through Statutory Instrument 1768, "The Plugs and Sockets etc. (Safety) Regulations"
This specifically requires socket outlets to comply with BS1363-2 plus amendments.The Plugs and Sockets etc. (Safety) Regulations 1994
These Regulations re–enact with modifications the provisions of the Plugs and Sockets etc. (Safety) Regulations 1987 (S.I. 1987/603) and make provision for the first time for certain requirements to be satisfied in relation to appliances.www.legislation.gov.uk
The standard defines not only construction requirements but also the plethora of tests that must pass for the design to be approved.
It requires products to be tested and approved (type testing) by an accredited test house, to the standard, before they are put on the market, and requires marking on the product to identify the test house to show compliance.
It is not permitted to CE mark plugs and sockets (now going to be UKCA since Brexit), 'self declaration' is not allowed for plugs and sockets, so the only legitimate route to market is through notified body testing.
The Socket under discussion has a spurious CE mark. I didn't see the mark of an accredited test house anywhere, and as Lucien commented on the 'instructions', I don't think any test house would have passed the instruction leaflet anyway.
I don't believe there is anything specific in BS1363-2 to say that multiple earth terminals must be connected (I could be wrong), so that doesn't help the cause, but it is plain that supplying these things is against regulations, so I believe Trading Standards could take action.
You are right, and Schedule 1 actually excludes sockets that incorporate another electrical device (eg usb or Wi-Fi). Must learn to read thoroughly!As I understand it only Standard Plugs need Notified body approval (Regulation 8) but Sockets fall under "Regulation 10 Electrical devices other than standard plugs" which only require testing. Agreed re: BS 1363-2, though, I can't find anything specific in that states that the earths must be linked, but the General requirement in cl.4 states that risks must be minimised so it is down to the lab interpretation of what this means. CE would still be needed if there is a CE Function like WiFi under Radio Equipment Directive/Regulations.
Also note in the MK instructions:I believe someone has mentioned "clean earth" sockets where the terminals are not linked, MK produce one but the terminals are marked different as can be seen here. I doubt however the accessory we are discussing has been designed for this purpose.
The issue I have with PSSR is that whilst it states "sockets" and includes sockets in regulation 3 "Interpretation", includes them in reg 4 "Electrical devices to which Part I applies", and goes on in para 6 "Requirements for electrical devices" therein it specified compliance for plugs to contain a BS 1362 fuse (in 6(2)) and in 6(1) requires compliance with reg's 8 or 10, these go on to not specify sockets!With my regulatory hat on ........
The UK 'law' on plugs and sockets is implemented through Statutory Instrument 1768, "The Plugs and Sockets etc. (Safety) Regulations"
This specifically requires socket outlets to comply with BS1363-2 plus amendments.The Plugs and Sockets etc. (Safety) Regulations 1994
These Regulations re–enact with modifications the provisions of the Plugs and Sockets etc. (Safety) Regulations 1987 (S.I. 1987/603) and make provision for the first time for certain requirements to be satisfied in relation to appliances.www.legislation.gov.uk
The standard defines not only construction requirements but also the plethora of tests that must pass for the design to be approved.
It requires products to be tested and approved (type testing) by an accredited test house, to the standard, before they are put on the market, and requires marking on the product to identify the test house to show compliance.
It is not permitted to CE mark plugs and sockets (now going to be UKCA since Brexit), 'self declaration' is not allowed for plugs and sockets, so the only legitimate route to market is through notified body testing.
The Socket under discussion has a spurious CE mark. I didn't see the mark of an accredited test house anywhere, and as Lucien commented on the 'instructions', I don't think any test house would have passed the instruction leaflet anyway.
I don't believe there is anything specific in BS1363-2 to say that multiple earth terminals must be connected (I could be wrong), so that doesn't help the cause, but it is plain that supplying these things is against regulations, so I believe Trading Standards could take action.
BS 1363-2The maximum load from a 2G 13A socket is usually taken as 20A. Where does this figure come from? Written into legislation somewhere, manufacturer's instructions or just a convention?