That is in BS 1363-2, "16 temperature Rise" 16.1.2 for fixed sockets, using Table 10. "loading of sockets for temperature rise test". - 2 outlets are loaded with 1*14A+1*6A, total nom. load on supply cable 20A.The maximum load from a 2G 13A socket is usually taken as 20A. Where does this figure come from? Written into legislation somewhere, manufacturer's instructions or just a convention?
Bring back ductor testing?...What we might have to rely on is the inadequate instructions. They mention a single earth wire, which cannot reasonably be understood as a wire to one terminal and a link to the other. Nor would a person skilled and qualified in electrical installation work be expected to know that a link is needed. Whilst such a person would test the completed work, which would reveal the issue in many cases, an end-of-radial tested at whichever socket has the CPC connected would show nothing abnormal. Even in RFC or middle of a radial, a fortuitous connection between the two terminals via the screws and back-box could yield satisfactory test results without the connection being adequately reliable.
@Pete999 have you not heard of Ductor testing?
High current low resistance testing.
Megger DLRO is a very common unit.
Mine is only 10A, but they are available up to 600A they stress the conductors to a higher level than the low current testing done by a typical MFT, or DMM.
They also offer a resolution much higher than those given by a typical MFT.
The way that EN 60204-1 is worded it is easily interpreted to require high current testing for all protective conductor networks.
A classic use for a Ductor was to test steel conduit when installed and utilised as the circuit cpc.
Very similar concept to the high current test used in PAT.Sounds like the high current earth bond test offered by some of the more expensive 'PAT' testers, including my fairly vintage Seaward one which does 25 amp low resistance testing.
Is ductor a trade name like Megger?
Very similar concept to the high current test used in PAT.
Ductor isn't a trade name AFAIK.
They are also known as I said above as high current low resistance testers, or micro/milli Ohmeters.
Megger DLRO10HD, DLRO200, Chauvin Arnoux CA6240/6255/6292 for example.
I have the DLRO10HD.
I have heard of Ductor testing, although I have never had the opportunity or experience of operating such a tester, was only asking out of interest.@Pete999 have you not heard of Ductor testing?
High current low resistance testing.
Megger DLRO is a very common unit.
Mine is only 10A, but they are available up to 600A they stress the conductors to a higher level than the low current testing done by a typical MFT, or DMM.
They also offer a resolution much higher than those given by a typical MFT.
The way that EN 60204-1 is worded it is easily interpreted to require high current testing for all protective conductor networks.
A classic use for a Ductor was to test steel conduit when installed and utilised as the circuit cpc.
I have heard of Ductor testing, although I have never had the opportunity or experience of operating such a tester, was only asking out of interest.
They are a 4 wire bridge measurement type device, so they automatically "null" out the lead resistance and you can even use them with two 50m wander leads within limits.Those testers look like they have an amazing level of accuracy. Reminds me of the short circuit location testers we used to use on circuit boards.
I always thought that as it started as "Con_ductor_ Tester", it was ductor, rather than "Con_ductor Tester_".I have a vintage one (naturally). I think the actual trade mark is 'Ducter' with an 'e', which is registered to Megger having started out as an Evershed and Vignoles product around the same time as the Megger.