length of cable runs
i=p/u
is this correct for lighting circuit of 1.5mm line and 1mm cpc
ze+R1+R2=zs
b6 mcb ze R1+R2
6.18ohms - 0.8ohms =5.38ohms
cable per meter = 0.03020ohms so 5.38ohms/0.03020=178.1M
does this mean my lighting circuit can be this length 178M and still be within zs value... cheeers if makes sense
That is on a BS 3036 fuse or BS 1361, not really used now on new installations, and is in absolute ideal conditions, should have some factors in there really even if only 0.95, will bring the length down.
You will probably also notice the length for 60898 MCB's which are more widely used nowadays, where the length comes down to 90, again in ideal situations.
yes it is, it is the next column down, but under cb/RCBO Type B/C/D, little confusing really, then if you look over to the right, it has a columns that state RCD or no RCD. all in all the figures seem to be same.
oh should say the next 2 'row's' down, before i get jumped on by the 'absolute correct crew'
That's better, never confuse rows and columns, it's a slippery slope and absolutely critical to the proper functioning of any table!
Yours,
Absolutely Correct Crue ;)
i=p/u,
Chr!s,