i=p/u

-
Arms
Joined
Dec 9, 2010
Messages
7,520
Reaction score
816
Location
Northern Ireland
is this correct for lighting circuit of 1.5mm line and 1mm cpc
ze+R1+R2=zs

b6 mcb ze R1+R2
6.18ohms - 0.8ohms =5.38ohms


cable per meter = 0.03020ohms so 5.38ohms/0.03020=178.1M

does this mean my lighting circuit can be this length 178M and still be within zs value... cheeers if makes sense
 
Last edited:
That is on a BS 3036 fuse or BS 1361, not really used now on new installations, and is in absolute ideal conditions, should have some factors in there really even if only 0.95, will bring the length down.
You will probably also notice the length for 60898 MCB's which are more widely used nowadays, where the length comes down to 90, again in ideal situations.
 
yes it is, it is the next column down, but under cb/RCBO Type B/C/D, little confusing really, then if you look over to the right, it has a columns that state RCD or no RCD. all in all the figures seem to be same.
 
oh should say the next 2 'row's' down, before i get jumped on by the 'absolute correct crew'

That's better, never confuse rows and columns, it's a slippery slope and absolutely critical to the proper functioning of any table!

Yours,

Absolutely Correct Crue ;)
 

Reply to length of cable runs in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
261
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top