This is a new one on me and not so sure how to tackle it. The customer is extending 3 bedrooms, ive quoted to install new lighting circuit for these rooms.

The existing circuit for the upstairs lighting does not have an earth and due to its routing it will need extending to fit round the shape of the new rooms. This existing circuit is supplying j.b's in the loft that spider to the bathroom, hall, and another bedroom; the customer will not agree to have these rooms rewired in t&e as it means making holes in the ceilings ! (----)

If I bring in a new feed to the existing J'bs how do I stand on reconnecting the existing circuits that dont have a cpc ?? Customer is adamant he dont want existing rewired but he wants the lights back on, I will IR each of these existing lighting circuits, if they pass I was thinking to make a note on the EIC that customer refuses rewire, and then reconnect.
 
The absence of a cpc means ADS is not complied with and this part of the installation is not Class II no matter what accessories are fitted as general purpose accessories are not Class II. The inclusion of an rcd is irrelevant. A disclaimer would hold little water as your client is probably signing something to which he/she has no understanding of.
 
The absence of a cpc means ADS is not complied with and this part of the installation is not Class II no matter what accessories are fitted as general purpose accessories are not Class II. The inclusion of an rcd is irrelevant. A disclaimer would hold little water as your client is probably signing something to which he/she has no understanding of.

Thanks for the info, although that part of the installation I will not touch. Im concerned with running a new supply (which will have a cpc) to the existing lighting jb which serves the existing lights and switches. Is this recommended or not was the reason for the post.
 
Thanks for the info, although that part of the installation I will not touch. Im concerned with running a new supply (which will have a cpc) to the existing lighting jb which serves the existing lights and switches. Is this recommended or not was the reason for the post.
No. Every part of the job that you include on the cert should be new wiring if you want to keep your nose clean. You can't use any part of the older wiring along any part of the circuit. New from start to finish. You will have created a new circuit for the rooms in question.

If the customer won't have that then toodle pip.
 
So your new cable will power the existing part of the circuit then also supply new parts of the circuit.

No there will be a new circuit for the new rooms, and I will remove the existing circuitry for these rooms from the existing JB.

The circuit that was feeding the upstairs lighting was chopped by the builder when he demolished the rooms and customer wants it reconnected as now there is no lights upstairs. So reconnecting to a JB in loft (with new t&e) that spiders to each room (not the new ones) in cable without cpc is what im considering.
[automerge]1568153046[/automerge]
Basically I wanna bring a new feed (t&e) to the loft JB. None of the existing outgoing wiring from this jb has cpc's.
 
Last edited:
you can repair like for like to old versions of the regs, but honestly however stubborn this guy is, once 2 or 3 professional sparks tell him he needs a rewire not a repair maybe he'll realise it's not a choice. "It's been fine for 50 years why change it" might take a while to convince, but with no lights he'll have plenty of time to think about it in the dark!
 
If the customer won't listen to reason, walk away.
If he thinks you are trying to rip him off, walk away.
If he is trying to cut cost to the minimum, walk away.
If you are unhappy with the job he wants you to do, walk away.
Let him get a bottom-feeder in, and walk away.
When he pleads with you to come back and sort his mess, walk away.
...and sleep soundly!
 
As soon as you run a new feed for old circuits you are responsible for it.......... walk
If I were you man up and tell him that it needs a complete Rewire and give price to reflect your hard work in doing so. If he doesn’t agree then tell him you can’t do the work because you don’t want to have a guilty conscience in doing something that is completely wrong and you will be liable for. You’ll be the one to blame if something went wrong start from scratch so you know it’s all safe and complient ?
 
If the customer won't listen to reason, walk away.
If he thinks you are trying to rip him off, walk away.
If he is trying to cut cost to the minimum, walk away.
If you are unhappy with the job he wants you to do, walk away.
Let him get a bottom-feeder in, and walk away.
When he pleads with you to come back and sort his mess, walk away.
...and sleep soundly!
So in essence "Walk away" is that what you are saying Pirate? lol, it's what I would do
 

Reply to Lighting circuit what to do in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K
  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top