The issue with the trees isn't that they shade all day rather they shade all the panels in the morning and then the panels start to come into sun about 11am and then by 2pm all the panels are in full sun. Thus from my understanding optimisers would help as they would allow us to generate an increasing amount between 11am and 2pm. Sound correct?
Re the white AC cable from the inverter to the generation meter. I measured it this morning and it's 1cm (10mm) in diameter. That's the whole cable including the white insulation. Thus I wonder if the cores are 1.5mm or 2mm at the most? It's a round cable. Thus do you think this is most likely to be the cause of the "Vac 10 min too high" error or "Frequency too high" that was causing the inverter to shut down?
Thanks
So, you are losing about 50% of max production per day in the summer, it will be worse in the winter as the sun is lower in the sky, therefore shading more panels.
It is highly probable that the "flex" they have used is causing the error codes mentioned, due to voltage drop.
I will try and explain, let's assume that your incoming voltage is on the high side, say, 250V, and at full power the Volt drop is 15V down your "flex", then for your inverter to match the mains voltage (well it has to go slightly over to push your PV power back into the grid), your inverter will have to raise it's voltage to 265V+, therefore exceeding it's set parameters causing it to produce the said fault codes.
This is just an example, and with some facts all of this can be calculated, but I hope this example gives you the understanding that you need.
Also, a little more technical this, your inverter may well be working on a particular input range from your panels, then when the shading clears, sometimes quickly, your inverter is still looking on or around the original power curve, which, may well be a long way from what your unshaded panels are now producing, not only can this cause some of your low output, it may cause a fault code too.
SMA inverters for example, have a setting called optitrac, which if enabled checks a wide range of input power curves to find the correct one for optimum output, some other makes of inverters have similar systems too.
As I have put before, all of your problems can be rectified, it is just a shame that you choose the company that you did to install your system.
Have you contacted them yet? If so what reply have they given you?