Was asked a question today and want to confirm my findings after reading the regs
we have a 1000A main supply (1000A ACB ) and from this we have 2 sets of supply conductors, 1 goes to a 600A Panel Board the other to a 400A Panel board with the tails being contained in a metal trunking, we plan to install a C/O Panel prior to the outgoing ways, the question I was asked was do the tails conform to the Regs, I believe that the overcurrent protection is provided by the Panel Board main switches with the fault protection coming from the 1000A ACB and also cosidering that they are installed in Metal trunking with no danger of Electric shock.
I believe that best procedure would be to split the supply near the origin with 2 MCCBs but we do not have the space.
The conductors are correctly sized.
Can anybody help
we have a 1000A main supply (1000A ACB ) and from this we have 2 sets of supply conductors, 1 goes to a 600A Panel Board the other to a 400A Panel board with the tails being contained in a metal trunking, we plan to install a C/O Panel prior to the outgoing ways, the question I was asked was do the tails conform to the Regs, I believe that the overcurrent protection is provided by the Panel Board main switches with the fault protection coming from the 1000A ACB and also cosidering that they are installed in Metal trunking with no danger of Electric shock.