HI all,

usually take tails form a MEB box to consumer unit no matter what the length as long as i can get the 50mm depth, builder has told me he wants it in SWA, ive told him its pretty much impossible to terminate it right if i use SWA also i run up the cavity with the tails and there is no way i can get SWA up there so will have to run inside up the wall which i hate doing, what do you guys do if using SWA??

Cheers
Grand
 
I've put metal switch fuses in meterboxes before but used the protek ones as there not too big, gland the swa into it then gland it into the metal ccu if possible, if its in a cupboard id just bring the armoured out and go surface into the bottom of the ccu, provide a pot of white paint if the customer doesn't like the look of it :)
 
Thinking about it further I wonder if GRP is non combustible? If so then it could be argued that it does comply.
As I said in #27 it is likely to char and not propagate any flame. These materials can have differing make up some of which do have fire resistant properties.
 
It maybe argued that the meter cabinet is outside the scope of bs 7671 so can't be used in the sense of a non combustible enclosure as bs 7671 sees it, then its maybe a departure which goes back round to what dave said but only slightly different reasoning.

Anyone still listening zzzzzzzzzzzz
 
If I hadn't lost the picture of the one I did before the non combustible rule came in then I wouldn't have posted that one.
Plus the KMF wouldn't have been upside down.
 
I've finally found some of the pictures i was looking for earlier. This job was done in early 2015 so had a completely legitimate plastic CU fitted.

This is what I mean about the flush box behind the CU
IMG_1985.JPG


And this is the supply end in progress, I can't find any pictures of it finished but you get the idea, and the KMF is the right way up!

IMG_1907.JPG
 
I've finally found some of the pictures i was looking for earlier. This job was done in early 2015 so had a completely legitimate plastic CU fitted.

This is what I mean about the flush box behind the CU
View attachment 37374

And this is the supply end in progress, I can't find any pictures of it finished but you get the idea, and the KMF is the right way up!

View attachment 37375
Ferrous box with live and neutral going through separate holes?

Edit going through timber or something else rather? thought I'd caught you out dave :)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Midlands
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Mains box to Consumer unit SWA or tails?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
79
Unsolved
--

Advert

Thread statistics

Created
grandfortune,
Last reply from
davesparks,
Replies
79
Views
19,021

Advert

Back
Top