Happens far to often sadly. We never stop learning, and we can all make mistakes but when I see things like this !!!! Sorry I rant yet again.

Rant away, you're spot on, but I can't see that as a mistake if someone was actually competent enough to measure the value in the first place and produce a certificate, it's pure incompetence and I see it every day of my PIR life!

Guys are testing and inspecting work without the underpinning knowledge to ensure that an installation is safe....
 
Exactly, and you can gaurantee, if you approached the guy he would say. Well the max is 1667 so its well within, anyway, its RCD protected.
And yes they will argue the point and call themselves qualified.
If the big book says jump over a cliff, they jump. The qualified man wears a parachute, he see's the bigger picture.
 
Exactly, and you can gaurantee, if you approached the guy he would say. Well the max is 1667 so its well within, anyway, its RCD protected.
And yes they will argue the point and call themselves qualified.
If the big book says jump over a cliff, they jump. The qualified man wears a parachute, he see's the bigger picture.
and if the RCD were to be faulty???????
 
and if the RCD were to be faulty???????

Then they can stick there 1667 where the sun doesn't shine cus somebody's gonna get hurt or worse.
Like many have said, this RCD thing is being relied on way to much.
I go with a good old solid earth any day.
 
RCDs come and go.the good old earth will still be here when we're all buried in it.
 
I questioned Castline systems about their default 1667 ohms and they say its OK. I disagree and update each line to show the "correct" values.
 
Its approved by NICEIC, says it all really. Due my annual review with Elecsa soon so will see what my assessor says, me thinks he and I will agree.

Maybe Castline will read this and understand the views of the professionals, rather that those of the corner cutters.
 
so.it's about 8-1 in favour of BS7671 values. bit like an arsenal defeat.
 
Its approved by NICEIC, says it all really. Due my annual review with Elecsa soon so will see what my assessor says, me thinks he and I will agree.

Maybe Castline will read this and understand the views of the professionals, rather that those of the corner cutters.
Have we verified this with them, or is that what Castline are saying?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
baldsparkies,
Last reply from
tester11,
Replies
81
Views
25,329

Advert

Back
Top