What table do I use in the on site guide to find the maximum Zs for a TT sytems? My Ze is 3.61 so they all be over anyway?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss maximum zs in the Australia area at ElectriciansForums.net
very true spin but you have to put in a 30ma RCd in for final circuits and it is the end of the final circuit you take te ZS from which is 1667 ohms
Not all final circuits require 30mA RCD protection, for instance: if the installation were a workshop, there may be no requirement for 30mA RCD protection other than on socket-outlets used to supply mobile equipment outdoors, and that could be provided by the use of an RCD socket-outlet. As such all the final circuits could then be covered by a 100mA RCD.very true spin but you have to put in a 30ma RCd in for final circuits and it is the end of the final circuit you take te ZS from which is 1667 ohms
Not all final circuits require 30mA RCD protection, for instance: if the installation were a workshop, there may be no requirement for 30mA RCD protection other than on socket-outlets used to supply mobile equipment outdoors, and that could be provided by the use of an RCD socket-outlet. As such all the final circuits could then be covered by a 100mA RCD.
I'm going to throw a spanner in the works now with regards to max Zs on TT when using RCD.
Max disconnection time for TT is 0.2 secs as Tel said earlier. However BS EN 61008 RCDs are designed to operate at ≤ 0.3secs at 1 x IΔn (I know in practice they usually go a lot faster than this)
To guarantee they operate in less than 0.2secs you need a residual current of 2 x IΔn, so 60mA for 30mA RCD and 200mA for 100mA RCD (see Table 3A on page 243 BRB).
So for 30mA max Zs would be 50V ÷ 0.06A = 833Ω and for 100mA max Zs would be 50V ÷ 0.2A = 250Ω
There is no requirement in BS7671 where TT systems must have RCD protection.remeber the thread is for TT system where rcd protection has to be fitted. TN-C-S systems allow for ommitions.
There is no requirement in BS7671 wher TT systems must have RCD protection.
Regulation 411.5.2 One or more of the following types of protective device shall be used, the former being preferred:
(i) An RCD
(ii) An overcurrent protective device.
The requirements for additional protection by use of a 30mA RCD apply to all installations, as do the exceptions.
Did you read Note 1 under 411.5.2??
The Ra value would have to be sufficiently low to allow the use of an overcurrent protective device, this can be achieved by using underground structural metalwork/earth plates etc. but in practice, it's almost impossible with the cheap, thin rods that I find are usually used on TT systems.
Don't think I can be bothered any more.
Perhaps it would be easier scotsparky if you ran through the reasons why you consider 30mA RCD protection is required on all circuits in TT installations, and why you believe the requirements for 30mA RCD protection are differnt for TT installations than for TN installations.
Yes JUD I am aware of Note 1 of Regulation 411.5.2