A
Andy B
What table do I use in the on site guide to find the maximum Zs for a TT sytems? My Ze is 3.61 so they all be over anyway?
ok so shall i put 1667 on the sheet for every circuit?
Thanks
Andy
Only on those circuits protected by a 30mA RCD.ok so shall i put 1667 on the sheet for every circuit?
Thanks
Andy
To be pedantic the maximum Zs allowed on a TT system, is not necessarily 1667Ω.
That figure only relates to wher 30mA RCD protection is installed.
Where 100mA RCD protection isinstalled, 500Ω is the maximum.