What table do I use in the on site guide to find the maximum Zs for a TT sytems? My Ze is 3.61 so they all be over anyway?
Ive read about ufer earthing, and it sounds interesing to say the least. Im going to speak to our electrical engineer about it to see if it can be applied to some of our new sites that are having civils done at the same time.
heres an example if no RCD is provided and there are high ZS readings due to a Ze of 30 ohms due to the earth rod how are you going to satisfy disconnection times, prove in the event of fault theat any voltage on exposed conductive parts is under 50v?
but your max. Zs figures are still related to the MCB e.g. 1.44 for a 32A type B, so all will fail. the 1667 value is only if you have a 30mA RCD fitted.
I thought that was only for TN systems, but I'm a little tired to get my head in the BRB now.![]()
at the very least, advise an up front RCD be fitted .
Good answers above but you really need to brush up on the reg's if you're doing EICR's-this is quite basic stuff and your client is paying for your expertise and advice.
Personally, I'd be strongly advising that a new CU is installed, providing that the wiring itself is acceptable, as technically we shouldn't be installing an up-front RCD to cover an entire installation. You will not be taking responsibility for the whole installation by doing so, you will merely be recording that the circuits you reconnect test safe for continued use.