hi my name is Gerry and i am putting together the parts required to fit my new shower which is a Triton 8.5 kw electric shower my consumer box is a MEM 2000 AD and i am not sure which RCD to purchase my friend is a sparky and is on holiday in Spain at the moment and i would like to have everything ready for him fit when he returns as he is doing me a favor, could somebody please advise me on the correct one to purchase, and also if possible as i am interested the formula used to work this out, regards Gerry..

I had a similar request a few weeks ago and contacted Eaton directly and they sent this info back to me:
[FONT=&amp]The Memshield 2 range of mcb’s and the rcbo “pods” are still in full production, and can easily be ordered. As mentioned they retro-fit straight into the consumer unit you have.[/FONT]
The only issue is the cost of the Memshield 2 and rcbo pod! Quite expensive!

You will need a 40 amp RCBO.
 
How much do the pods go for? I work on a maintance contract currently and they over ordered on a job so I have a fair few knocking around
 
Gerry I'm going to sound brutal here and if I'm wrong I apologise in advance. I don't believe that this "sparky friend" of yours exists. I reckon you're a DIYer who wants to have a go at this himself and to a point I applaud you for being willing however, this is notifiable work, regardless of that, electricity is dangerous in untrained and unskilled hands.
Electricians are usually cheaper and less traumatic than funerals mate, I can't believe the advice you're getting.
 
How much do the pods go for? I work on a maintance contract currently and they over ordered on a job so I have a fair few knocking around
Yes that's just the image we want to give isn't it. Don't worry about the materials Mr Client I'll just nick them from work.
 

Reply to mem 2000 AD consumer box, rcd for an 8.5 kw shower? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
190
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
3K
As someone who is in the process of registering with napit for the first time reading their response they sent to OP by email about the “eicr”...
Replies
61
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top