Meter Tails 16mm 0r 25mm | on ElectriciansForums

Discuss Meter Tails 16mm 0r 25mm in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

haj

-
Arms
Joined
Nov 6, 2008
Messages
256
Reaction score
45
Location
East Yorkshire
Talking with a collegue today regarding meter tails.I went to look at a c/u change 80A main head on 16mm Tails i said should be 25mm but he said 16mm was ok 25mm for 100A main head. Whats the word out there with you good men ?
Cheers :)
 
Always go for the better option with cable sizes. I would personally never use 16mm whatever the incomer fuse. Even if you know it's 60A or 80A, pretend it's 100A and put in 25mm2 tails ( double insulated ). The 17th Ed. recommends that anyway whatever.
 
Thanks guys i quoted OSG it says SHOULD be 25mm not must be 25mm he says leave them alone i think change them.
quite right haj, exact wording is

"polarity should be indicated by the colour of the insulation and the minimum cable size should be 25mm2"

theres 2 shoulds in that statement. would your mate ignore the first should the sameas he would the second should :eek::eek:

25mm it is then ;)
 
Talking with a collegue today regarding meter tails.I went to look at a c/u change 80A main head on 16mm Tails i said should be 25mm but he said 16mm was ok 25mm for 100A main head. Whats the word out there with you good men ?
Cheers :)
hi i assume that it was a house you went to so has to be 25mm .also double insulated hope this helps.
 
I always use 25mm tails, just remember to upgrade the bonding cables to suit.
The meter tail size is dependant on the cutout fuse rating as far as i `am aware.
 
You are supposed to get them to pull the fuse (its their equipment) but i always do it my self problems start at the main fuse if youre up rating the tails from the meter to the consumer unit then you should also change them from the incomong supply point ( the fused inlet)Probably stating the obvious burt rememmber the meter is wired live neutral neutral live good luck you obviously can't seal the job but to be honest most work i come across the meter is never sealed any way good luck phil S
 
Do you get leb in to pull fuse or are we aloud to disconnect from there meter
Peter if you are in any dout as to weather to remove the suppliers cut out. dont be. Basicly the electricity at work act says that every installation has to be provided with a means of isolation for safe working. So if the supllier has provided a means of isolation ie a swich or the meter with a built in isolator (not designed to be switch under load) then all is fine but if they have only provided a cut out and meter then they can not argue why you have cut their seal and removed the fuse. what do they expect you to change the tails LIVE!?????
Hope this helps
Regards
AJ;)
 
Thanks gentlemen as far as pulling the cut out as said earlier JUST DO IT we need to stay safe dont we:D 25mm & 16mm earth it is then !
I digress i have been asked to wire a loft conversion my questions are is it ok to extend the upstairs ring and lighting or should i take a couple of new direct feeds from the board not so easy but possible i think.Do i need to beware of any regular problems that pop up with loft conversions ?
Cheers Guys
 
Yes in an ideal world, but its just not reasonalbe practicable is it. so you are a good boy and phone them every time you want to change some tails and you sit around waiting for them to pop out and do it for you. Don't think you would win many jobs if you are chargeing on the costs??. They have obvsioly seen a problem with the old units and thats why now they install either a swicth or the meter with the isolator built in.
Many Thanks
AJ:eek:
 

Reply to Meter Tails 16mm 0r 25mm in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
517
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top