no, actually, no real naked ladies, but

I done a EICR or PIR actually on an old house with apparent TT set up for earthing. 6mm earth cable coming up from the door step to the 3036 board. I disconnect the earth cable and do a Ze. Reading? - 0.11!!!!!!! Test between Live and neutral, same reading.

Can't see where connection made between neutral and earth. Any suggestions?
 
it wont be TT....
them rods were left connected no doubt.....but it aint TT is that....it all points to tncs....

Yes Glenn the readings DO suggest TNC-S but do any of you experts have any suggestions WHERE the connection between neutral and earth have been made? As I have stated,, concentric cable coming in to fairly new service head. Single 6mm earth cable going down to ground by front door. No earth from service head to DB. 0.11 Ze. Weird.
 
i`m wondering if theres a buried joint someware.....
does the service cable come up from the ground....or is it clipped to the wall as you have stated its an overhead supply...
caus i`m just thinking if theres a scotchcast onto the neutral someware.....and the earth is coming off that....
just speculative mind...
 
No need to shout Voltz, I am simply suggesting that the earth wire from the rod may be strapped to either the gas or water main on its route from the rod to the DB?????????

Its hard to see the job from my lounge............

I'm not SHOUTING!

HAHA

The apparent earthing is from the front step, by the DB and the meter.

The gas intake is 5 meters to the left in the lounge. the water intake is way back in the rear of the property. I followed the procedure for doing a Ze, i.e. DISCONNECT the incoming earth and test between it and the supply. result is 0.11 ohms which for an apparent TT system, seems low, I want to know if anyone has experienced a similar setup, and if so, where was the earth connected to the neutral as this is (same readings L-N / L-E).

Thanks.
 
i`m wondering if theres a buried joint someware.....
does the service cable come up from the ground....or is it clipped to the wall as you have stated its an overhead supply...
caus i`m just thinking if theres a scotchcast onto the neutral someware.....and the earth is coming off that....
just speculative mind...

Cable comes in from overhead Glenn. Just Live and Neutral. Comes in top of the front door with earth separate going down to front door step..
 
Disconnect the earth at the rod end and using a wander lead test the rod directly Voltz.

You may be surprised and find the rod giving you a VERY low reading for TT, testing the rod direct will verify the Ra at least at the property to rule out this .........
 
Disconnect the earth at the rod end and using a wander lead test the rod directly Voltz

appreciate the advice, but a little impracticable TBH. Not My House and given the readings, not justifiable to start smashing about a customers residence for what? A better reading! FFs I'm after advice about why the readings are so good!
 
Disconnect the earth at the rod end and using a wander lead test the rod directly Voltz.

You may be surprised and find the rod giving you a VERY low reading for TT, testing the rod direct will verify the Ra at least at the property to rule out this .........
he has done syk...
its just strange (but not impossible) to be getting .11 on a TT....
the same on Zpe & Zpn however can only really mean one thing
 

Reply to naked ladies!!!!! in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Replies
5
Views
953
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top