old board= under sized and a dual mains switch board
new board= more ways to split accordingly and RCD protected as per regs.
So how is that like for like????
 
The rcbo had melted out and wouldnt reset! as it had been running half the house for quite some time! it was only 32a.
He wanted his power back and there were no other spare ways available to get him going again as most of the circuits were doubled up anyway. I dont think i would of found a mains switch for a board that old.

This is a wind up yeah....
 
Wish i had never got involved in this job to be honest but you live and learn i guess!
Most of my customers would be happy knowing their house is safe but others just like to scrape by!
He knew the house was dodgy and thats why we agreed to do a cu change and test to check for other hidden surprises.

You have learn't the lesson ? Perhaps if you looked for the "surprises" which you have had no problems finding AFTER:mad2: you change the board ? Or did you think your customer would just agree to the additional works and cost ?
 
Last edited by a moderator:
You still haven't said why the garage circuit failed or what it failed?and i fail to see a lack of isolators for the fan and fridge as unsafe and dodgey

2.5 3core swa running a board in the garage!! about 12 double sockets, a spur and lighting. also the mains switch of the garage borad has been taken out so no means of local isolation.
holes big enough to fit 2 finger in!!?
 
db2 in garage is run in 2.5 3c swa with a million sockets and light etc also the mains swith on db2 is non existent and big hoes in sides etc. What is the problem with it feeding a million sockets?? Where is the problem here?? There is one vital bit of information you are missing

no fan iso in bathroom - Whats the problem.. May have complied at time of install
no iso for integral fridge - Ditto
cooker (GAS FAN ASSISTED) is run in 6mm to a sw fused spur where it is down graded to 13amp with 1.5 t&e to socket for spark. tried putting a 5amp in instead but as soon as the cooker is played with it pops the fuse. Why fuse down to 5a whats wrong with 13a

As above
 
next time tell us the whole story not just little bits, because you just sound like you have no idea on what you are doing and that by the sounds of it you don't, so you must go to all your jobs and just say straight away oh you need to update your board,
 
This is a wind up yeah....

It was dangerous the way the board was! making it RCD protected couldnt make it any worse!! it had 1.0mm lighting off 20a mcbs the lot!

He wanted power back to his house and i couldnt see any other way of doing it safely! i did warn him before i started that if the rest of the house is anything like the board it wasnt looking good!!

I got the job as a call out as half his house had no power!!
 
next time tell us the whole story not just little bits, because you just sound like you have no idea on what you are doing and that by the sounds of it you don't, so you must go to all your jobs and just say straight away oh you need to update your board,

Excuse me??

What would you have done then?
 
2.5 3core swa running a board in the garage!! about 12 double sockets, a spur and lighting. also the mains switch of the garage borad has been taken out so no means of local isolation.
holes big enough to fit 2 finger in!!?
got a couple of blanks? Sorted!
 
If the board was in such a bad state wouldnt you change it? i know i wouldnt want to put my name to that old board!
The holes i know can he filled with blind grommets but i thought having local isolation would be important!!! also having a million sockets isnt a problem its the tumbly dryer and freezer, fridge and others plugged into it!!!!!!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
New consumer installed but failed inspection
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
66

Advert

Thread statistics

Created
k17byo,
Last reply from
geordie,
Replies
66
Views
7,634

Advert

Back
Top