Hi,

I’d appreciate views on the fuse board.

It’s been completely rewired and I’m unhappy with the quality.

I’ve messaged him about it and described the board as a complete mess, and poor workmanship ship. For entry for the 25mm cables and 16mm tails he used the knock out but didn’t bother using the plastic cable holder - which is a couple of quid.

Also with the cables coming in through the back, there is no plastic or anything so the metal of the board could rub against the metal of the board.

his reply is below

a. - there is a reason why cables shouldn't be perfectly arrange in the fuse box because it could create electromagnetic field resulting in humming sound in the fuse box- you would probably think that's ridiculous ! But it's a fact!


Quite frankly I’m shocked, would you be happy with the work, paying over 4k? And supplying the board all second fix items etc? So basically 5k?

He has also created 5 additional lighting circuits downstairs, I live in a three bed terraced house.

1) for 6 down lights in a 2.5m x 2m room.
2) just the ground hallway light.
3) the lounge dinner, two lights and two wall lights.
4) a porch light and floodlight.
5) under stairs light simply 2 lights.

His reply is that it is is better… but then it’s all on a dual rcd so it doesn’t really help in my opinion.

We agreed the whole of downstairs on a circuit except the hallway on a separate one. (He said that was best practice.

I’ve attached photos and the pieces that I believe should go there. One is too big.
 

Attachments

  • [ElectriciansForums.net] New rewire and fuse board - views on work.
    524CC7D8-A048-4BC8-90DD-E2F06AE59EFF.jpeg
    505.9 KB · Views: 158
  • [ElectriciansForums.net] New rewire and fuse board - views on work.
    C4DC1E06-3B9A-41F4-9248-9C59CC8D36C1.png
    325.7 KB · Views: 139
Where are you in London.
South west London.

I’m not a cheap skate or whatever, so if someone is prepared to have a look over things even to say, it all appears fine - it’s just a mess then that would be fine.

It’s worrying me about the earth cable to SPD, has it been fitted incorrectly? If I’m honest I can’t recall seeing that yellow wire in the box at all ?
 
I'd certainly be interested to know the outcome. I've only ever fitted one of those and had to add the module myself, and it came with a bit of 6mm CPC that obviously I went looking for a home for.
But I've seen a couple on EICRs and may have messed up myself as my photo of one of them doesn't have a CPC connection.
I'm wondering if some sheds are assembling the populated boards themselves and getting it wrong....
I've emailed hager, I'll update when I have news
 
I supply two quotes when quoting a board, one for dual rcd, one for full rcbo, with a strong recommendation to fit the rcbo board and with the continuing drop in rcbo costs this is getting an easier argument to win in most cases

I would say I get about 60% go with the rcbo board( when it’s their own property mostly)

for rentals they always seem to go with the cheapest option, even though I explain it’s potentially a false economy

I earn the same profit to fit either, I would not like to risk losing potentially 40% of the work by refusing to fit a dual rcd board, that’s their choice

I understand your reasoning, but wouldn't be inclined to do the same.

A few years back I'd have considered this a fair approach, but believe the cost of technology is now sufficiently low to dispense with dual RCD options (not to mention regulatory advice). With homes continually being filled with more and more gadgets, along with appliances intended to leak current to earth, I don't consider a dual RCD set up as providing sufficient capacity for the near future. Most homes are unlikely to experience nuisance tripping because of RCDs protecting multiple circuits, but I'd rather not make that assumption on behalf of homeowners. Providing an explanation of benefits is all well and good, but a significant number of homeowners won't grasp the principles behind your recommendation of a slightly more expensive option.
 
Here's a picture of a Fusebox CU with compact RCBOs recently installed by me , this wouldn't cost an awful lot more than the dual RCD Hager board you specified and is good quality. I think how a CU is fitted/connected up gives a fair idea of an electricians attitude to their work and any decent Electrical Tradesperson would produce something like this.
This maybe me being a bit picky but

How long are those tails ? the ones going through those big holes near the twisted rcbos 🤣
 
Hi guys I’ve included more pics including that of the SPD. (In my non electrical brain it shows an earth coming out from the top of the SPD but there there are the two bit coming out. As I said when we opened the box I never saw an earth wire in the box nor connected to the SPD.
 

Attachments

  • [ElectriciansForums.net] New rewire and fuse board - views on work.
    0A835E04-484E-4A5A-9397-0850C7B20D64.jpeg
    735.9 KB · Views: 87
  • [ElectriciansForums.net] New rewire and fuse board - views on work.
    860B4D67-24A9-4F37-B455-C7CD8D351AB2.jpeg
    723.1 KB · Views: 79
  • [ElectriciansForums.net] New rewire and fuse board - views on work.
    DDA75C56-E3AC-4577-8D45-7C308950156D.jpeg
    723.1 KB · Views: 76
  • [ElectriciansForums.net] New rewire and fuse board - views on work.
    AE5BB181-B9BA-40DE-A7C8-FE442B9E876F.jpeg
    696 KB · Views: 81
  • [ElectriciansForums.net] New rewire and fuse board - views on work.
    E52836F8-7BA3-4787-BBAB-299A124E11F5.jpeg
    712.1 KB · Views: 90
  • [ElectriciansForums.net] New rewire and fuse board - views on work.
    BC15A321-0AD8-451A-BE1A-0238DB5A2C4F.jpeg
    929.6 KB · Views: 95
I also agree with the opinion , that there is nothing wrong with fitting Dual RCD DB. It's mainly matter of convenience for me, when using RCBO's instead of dual RCD, in case of a fault. At the moment we are finishing residential apartments complex, using exactly the same Hagger DB's. I must have tested 300 of them so far. Regarding the mentioned above DB job, it's cheaply done, but this very common, when a client choses the cheapest offers. Normally, I would use gland for the meter tails and supporting clips. Cables contained in 50x50mm trunking(or bigger) , and using metal bushes/lockrings instead of the knockouts. All gaps/cable entry sealed with fire mastic. And at the end - all connections within DB tightened with torque screwdriver by manufacturer's specifications(nearly nobody is doing that, but yesterday was called out to sort a problem because of loose busbar connection in DB). Also I would leave a spare MCB before the 1st RCD(for security alarm/fire alarm/ disability / garrage DB circuits).

There are many things in the OP's board that a lot of electricians would do differently, but I tried to limit criticism to issues that breached actual regulations and avoid stating what might be considered best practice.
 
Hi guys I’ve included more pics including that of the SPD. (In my non electrical brain it shows an earth coming out from the top of the SPD but there there are the two bit coming out. As I said when we opened the box I never saw an earth wire in the box nor connected to the SPD.
This is the same as the one I fitted. I think it connects to earth via the steel enclosure and din rail, but I have emailed hager for clarification and will update when I have news
 
This is the same as the one I fitted. I think it connects to earth via the steel enclosure and din rail, but I have emailed hager for clarification and will update when I have news
Hi well like you I had no cpc cable in the box or coming out of it, and from your pic mine looks the same if that is of any help.

Looking into RCBO’s now - is there any reason why the Hager enclosure couldn’t be used ?
This is the exact one Design 10 - 14 Way 100A Dual Split Consumer Unit c/w 2 RCDs (Type A) + SPD | Hager (VML914CUSPD) - https://www.tlc-direct.co.uk/Products/HGVML914CUSPD.html
 
There are many things in the OP's board that a lot of electricians would do differently, but I tried to limit criticism to issues that breached actual regulations and avoid stating what might be considered best practice.
Hi, could you please tell me best practice ?

I’ve seen that people install a 100 amp isolator before the board.

Forgive me I don’t want to be rude to anyone, but is it possible he passed after doing one of these short courses, like the 3 week ones, rather than an apprenticeship / or the normal way of college/ training etc.
 
Hi, could you please tell me best practice ?

The post I was responding to mentioned several ways in which they'd have approached this board differently and I'd have taken a similar approach, but not doing so isn't a breach of any regulation.

Containment of cables would give a more aesthetically pleasing look to the installation, but sheathed cables such as the twin and earth used in domestic installations does not need to be contained.

The issues to which you can legitimately raise objections have already been covered: Power and lighting should be split across both RCDs, so loosing one bank of circuits will ensure either power or light remains in any given area of the home. Cables (including incoming tails) should be suitably supported and restrained - there are many ways in which this can be done, including the simple cable clip. If there is sufficient space for finger access where tails come in the bottom, then this should be filled. Cables should be protected from metal edges as they come into the board, which can be remedied through the use of grommet strip.

I know not all issues will be covered in the above paragraph, as I'm working from memory of what I read last night, but am trying to draw a clear distinction between how electricians might approach this job and what is actually required from a regulatory perspective.


Edit: An isolator after the meter is very helpful for future work or maintenance, but no regulation mandates this additional means of isolation.

As for training? I couldn't comment - many time served electricians turn out shoddy work and there are also electricians who came to the industry through a short course and go on to turn out exemplary work. Knowledge is very useful, but can be renered pointless if not accompanied by a good work ethic.
 
Last edited by a moderator:
So my research seems to indicate that RCBO's can fit within the board. They are listed as an accessory by TLC.

The board code brings up that is High Intensity - how many RCBO's I can fit, I don't know. A single RCBO from TLC is nearly ÂŁ30 on its own.
Should I get an electrician to change everything to RCBO (if possible). If not should I get sockets and lights on their own RCBO, (the kitchen is on its own board, so if the new board trips I still have light and power downstairs).

I'm also getting a car charger, and solar, I assume these are both high risk items. So I should spend the extra and also put them on a RCBO on the main Hager Board ?

Or should I spend even more, and get the car charger, and solar, on its own RCBO board, with surge ?
 
So my research seems to indicate that RCBO's can fit within the board. They are listed as an accessory by TLC.

The board code brings up that is High Intensity - how many RCBO's I can fit, I don't know. A single RCBO from TLC is nearly ÂŁ30 on its own.
Should I get an electrician to change everything to RCBO (if possible). If not should I get sockets and lights on their own RCBO, (the kitchen is on its own board, so if the new board trips I still have light and power downstairs).

I'm also getting a car charger, and solar, I assume these are both high risk items. So I should spend the extra and also put them on a RCBO on the main Hager Board ?

Or should I spend even more, and get the car charger, and solar, on its own RCBO board, with surge ?
The best thing to do is get another sparky in (A decent one) and let them plan it for you.

You certainly don't need all those circuits on separate rcbos.
 
The best thing to do is get another sparky in (A decent one) and let them plan it for you.

You certainly don't need all those circuits on separate rcbos.

Also unlikely to gain any benefit from the additional expense of changing to RCBOs and sourcing new busbar. I'd be inclined to leave the current set up in place, unless cumulative earth leakage happens to cause nuisance tripping (of which there have been no reports so far).
 
So my research seems to indicate that RCBO's can fit within the board. They are listed as an accessory by TLC.

The board code brings up that is High Intensity - how many RCBO's I can fit, I don't know. A single RCBO from TLC is nearly ÂŁ30 on its own.
Should I get an electrician to change everything to RCBO (if possible). If not should I get sockets and lights on their own RCBO, (the kitchen is on its own board, so if the new board trips I still have light and power downstairs).

I'm also getting a car charger, and solar, I assume these are both high risk items. So I should spend the extra and also put them on a RCBO on the main Hager Board ?

Or should I spend even more, and get the car charger, and solar, on its own RCBO board, with surge ?

Even pairing down the number of circuits, you're looking at ÂŁ300+ additional expenditure and for what gain?

EV charge point may present an issue with current installation, but there are a number of ways in which that issue could be overcome.

I'm not telling you not to make this change, but asking you to consider whether or not it's worth spending money on. One benefit would be that any fault to earth causes tripping of a single circuit, but is that really essential to you?
 

Reply to New rewire and fuse board - views on work. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
717
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Pretty common for lights and sockets to get a Re-wire and the Eco7 circuits usually storage heaters /water heater to remain left as was. As for...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top