I'm doing a low ohnms continuity test. I'malso, what continuity test are you doing
Neon on switch between L and N?
also, what continuity test are you doing?
What exactly do you mean by not getting a continuity reading? how low was the IR Test? cooker sockets is working also?Not getting a continuity reading on the cooker circuit. I'm doing I.r. test and its low between l. N. Any ideas what the issue could be.
The cooker sockets is working also.
I have mate. I'm not getting a reading. When I link line and neutral I get 0.10 ohmsWhat reading are you getting. You will only get a line to cpc reading if you have connected a link across them.
I have mate. I'm not getting a reading. When I link line and neutral I get 0.10 ohms
Zs for the installion is OK. But everything fine apart from no continuity on the line earth at cooker. Obviously if there's a fault the breaker might to work
Sound mate.
So the means of fault protection wouldn't function then. Additional protection might. But issue needs solving.But everything fine apart from no continuity on the line earth at cooker.
Test cont between LN LE NE IR the same and publish the results,Zs for the installion is OK. But everything fine apart from no continuity on the line earth at cooker. Obviously if there's a fault the breaker might to work
Sound mate.