no earth on lighting r1+r2 what do you put on sheet | Page 2 | on ElectriciansForums

Discuss no earth on lighting r1+r2 what do you put on sheet in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

what about metal back boxes
if you refer to switch boxes, they were not exposed and the plate fixing screws were either plastic or the back box had nylon screw lugs.
 
Yes. And C3 on those circuits with text explaining the reason. Providing no metal/class I fittings.

PS. It's not a certificate. It's a report.
 
You can install it but Needs agreement of client.
Read chapter 10 here
http://www.----------------------------/mediafile/100423440/Best-Practice-Guide-1-Issue-3-.pdf
 
It does not state that you can do it with the clients agreement.

It states that you need to try and get the client to agree to either rewiring the lighting circuits or the addition of a CPC installed to all accessible points. If the client refuses this then a fall back would be to offer to replace all class 1 accessories with class 2 or the circuits can not be reconnected if this is also refused then.

AS AN ABSOLUTE LAST RESORT then a risk assessment should be carried out with the additional tests listed. If any of the additional test fail then thoes lighting circuits can not be re connected.

On completion a record of any non compliances must be made in the comments box

I would also add the risk assessments carried out with the results, this may require an additional sheet of paper attached to your report documenting the chain of events and the clients refusal to carry out remidal works and the additional risk assessment tests and results.

I would have thought that this senario would be down to replacing the CU due to damage or fault as if the client refused to renew the circuits at the same time as a CU upgrade you would probably walk away as alarm bell would start to ring.

At the end of the day as you are the technically competent person offering advice you carry the can and can not rely on a defence that the client was happy for me to do it.
 
Last edited:
you write what you are saying . got a call out to job where their was a fault no cpc any where
metal back boxes and plastic fronts in some rooms. and in others rooms not one back box just the plate screwed to the wall
told the owner rewire of lights . she was more concerned about her bloody alarm .I asked her the alarm was fitted by a spark she said
no bonding gas or water I then walked away
 
Last edited:

Reply to no earth on lighting r1+r2 what do you put on sheet in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
829

Similar threads

The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
999
Was there any toast to go with the beans? Just joking I think that you ment beams and not beans I am dyslexic and simple mistakes tend to jump out...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top